8.5.5.3* Obstructions That Prevent Sprinkler Discharge from
Reaching the Hazard. Continuous or non-continuous obstructions
that interrupt the water discharge in a horizontal plane
more than 18 in. (457 mm) below the sprinkler deflector in a
manner to limit the distribution from reaching the protected
hazard shall comply with 8.5.5.3.
8.5.5.3.1 Sprinklers shall be installed under fixed obstructions
over 4 ft (1.2 m) wide such as ducts, decks, open grate
flooring, cutting tables, and overhead doors.