8.5.5.3* Obstructions That Prevent Sprinkler Discharge from Reaching the Hazard. Continuous or non-continuous obstructions that interrupt the water discharge in a horizontal plane more than 18 in. (457 mm) below the sprinkler deflector in a manner to limit the distribution from reaching the protected hazard shall comply with 8.5.5.3. 8.5.5.3.1 Sprinklers shall be installed under fixed obstructions over 4 ft (1.2 m) wide such as ducts, decks, open grate flooring, cutting tables, and overhead doors.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)