There are many heads listed for exposure window protection, but not window protection for interior or the building. I think TYCO has the only window sprinkler that gives you an equivalent to 1 hour wall rating for glass, at this time.
7.8.8.4 For protection of window and similar openings, listed window sprinklers shall be positioned within 2 in. (50.8 mm) of the top of the window sash in accordance with Table 7.8.8.4. Listed window sprinklers for exposure protection cannot be used for interior windows in a rated wall. Table 7.8.8.4 Position of Window Sprinklers Width of Window Nominal K-factor Nominal Distance U.S. Metric from Window Up to 3 ft 2.8 40 7 in. >3 to 4 ft 2.8 40 8 in. >4 to 5 ft 2.8 40 9 in. 5.6 80 12 in. >5 to 7 ft 11.2 161 12 in. Two 2.8 40 7 in. >7 to 9.5 ft 14.0 202 12 in. Two 2.8 40 9 in. >9.5 to 12 ft Two 5.6 80 12 in. For SI units, 1 ft = 0.3048 m. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Friday, April 02, 2010 7:02 PM To: [email protected] Subject: RE: WINDOW SPRINKLERS Reliable Model FM for one. They are not listed to make the glass 1 hour rated, but they are listed for exposure protection. Greg McGahan Living Water Fire Protection (850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Thom McMahon Sent: Friday, April 02, 2010 10:01 AM To: [email protected] Subject: RE: WINDOW SPRINKLERS Who else has a listing? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Subject: RE: WINDOW SPRINKLERS You know there are window sprinklers other than Tyco's. Greg McGahan _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)