So long as the water can sheet down the glass from point of contact at the top, 
to the bottom of each panel, you can do it.  As Thom said, refer to the data 
sheet for placement requirements; if the panels are less than 6' wide, you will 
likely have to baffle or separate the spirnklers in some manner so they don't 
cold-solder.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Thursday, April 01, 2010 12:52 PM
To: [email protected]
Subject: RE: WINDOW SPRINKLERS

George,

The objective is that the entire surface of the glass be wetted.  

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Medina Jr
Sent: Thursday, April 01, 2010 3:31 PM
To: [email protected]
Subject: Re: WINDOW SPRINKLERS


I  apologize for not being more clear, the 2½" mullions are vertical and was 
asking if each panel required separate sprinklers for them exceeding 1".

Thanks,
George Medina Jr. 




-----Original Message-----
From: Steve Leyton <[email protected]>
To: [email protected]
Sent: Thu, Apr 1, 2010 12:22 pm
Subject: RE: WINDOW SPRINKLERS


You're not allowed horizontal mullions or molding.   The glazing can be 
eparated by vertical mullions so long as each panel has its own sprinkler, but 
orizontal bumps are a deal-breaker.
Steve Leyton
rotection Design & Consulting
an Diego, CA


----Original Message-----
rom: [email protected] 
[mailto:[email protected]] 
n Behalf Of George Medina Jr
ent: Thursday, April 01, 2010 12:19 PM
o: [email protected]
ubject: WINDOW SPRINKLERS

orum,
NFPA-13 (2007) Sec.7.8.8.2 
here window sills or similar features result in recesses or projection 
xceeding 1" in depth, separate sprinklers 
hall be provided for each window on each level, regardless of wether protection 
s being provided for windows 
r complete walls.
Would 2½" mullions spaced at 4'-0" on center with the window height at 9'-0" 
with no sills) be considered a similar feature?
and require separate sprinklers? it seems like it is addressing horizontal 
rojections only.

eorge Medina Jr. 
_______________________________________________
prinklerforum mailing list
[email protected]
ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
Put the word unsubscribe in the subject field)

__________ Information from ESET NOD32 Antivirus, version of virus signature 
atabase 4946 (20100315) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com


__________ Information from ESET NOD32 Antivirus, version of virus signature 
atabase 4946 (20100315) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com

______________________________________________
prinklerforum mailing list
[email protected]
ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4946 (20100315) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4946 (20100315) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to