You're not allowed horizontal mullions or molding.   The glazing can be 
separated by vertical mullions so long as each panel has its own sprinkler, but 
horizontal bumps are a deal-breaker.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Medina Jr
Sent: Thursday, April 01, 2010 12:19 PM
To: [email protected]
Subject: WINDOW SPRINKLERS


Forum,

NFPA-13 (2007) Sec.7.8.8.2 
Where window sills or similar features result in recesses or projection 
exceeding 1" in depth, separate sprinklers 
shall be provided for each window on each level, regardless of wether 
protection is being provided for windows 
or complete walls.

Would 2½" mullions spaced at 4'-0" on center with the window height at 9'-0" 
(with no sills) be considered a similar feature?
 and require separate sprinklers? it seems like it is addressing horizontal 
projections only.


George Medina Jr. 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4946 (20100315) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4946 (20100315) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to