See TYCO data Sheet TFP 620.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Medina Jr
Sent: Thursday, April 01, 2010 1:31 PM
To: [email protected]
Subject: Re: WINDOW SPRINKLERS


I  apologize for not being more clear, the 2½" mullions are vertical and was 
asking if each panel required separate sprinklers for them exceeding 1".

Thanks,
George Medina Jr. 




-----Original Message-----
From: Steve Leyton <[email protected]>
To: [email protected]
Sent: Thu, Apr 1, 2010 12:22 pm
Subject: RE: WINDOW SPRINKLERS


You're not allowed horizontal mullions or molding.   The glazing can be 
eparated by vertical mullions so long as each panel has its own sprinkler, but 
orizontal bumps are a deal-breaker.
Steve Leyton
rotection Design & Consulting
an Diego, CA


----Original Message-----
rom: [email protected] 
[mailto:[email protected]] 
n Behalf Of George Medina Jr
ent: Thursday, April 01, 2010 12:19 PM
o: [email protected]
ubject: WINDOW SPRINKLERS

orum,
NFPA-13 (2007) Sec.7.8.8.2 
here window sills or similar features result in recesses or projection 
xceeding 1" in depth, separate sprinklers 
hall be provided for each window on each level, regardless of wether protection 
s being provided for windows 
r complete walls.
Would 2½" mullions spaced at 4'-0" on center with the window height at 9'-0" 
with no sills) be considered a similar feature?
and require separate sprinklers? it seems like it is addressing horizontal 
rojections only.

eorge Medina Jr. 
_______________________________________________
prinklerforum mailing list
[email protected]
ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
Put the word unsubscribe in the subject field)

__________ Information from ESET NOD32 Antivirus, version of virus signature 
atabase 4946 (20100315) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com


__________ Information from ESET NOD32 Antivirus, version of virus signature 
atabase 4946 (20100315) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com

______________________________________________
prinklerforum mailing list
[email protected]
ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to