Yes there is now....Tyco I believe. We priced it recently and I was proven 
wrong when I said there wasn't one. It has only been listed for a few months.

Greg McGahan

Living Water Fire Protection
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Tuesday, April 13, 2010 5:31 PM
To: [email protected]
Subject: Re: Pipe Wrapping

there IS listed heat tracing for sprinkler system but there are NONE  
yet listed for use on BRANCH LINES.  At least not the last time I  
checked.

Roland

On Apr 13, 2010, at 3:00 PM, [email protected] wrote:

> Thank you for the info.
> I just read a tech bulletin from the NFSA this morning, and I  
> thought it said they were unaware of listed trace systems.
> This shows the importance of asking multiple sources for opinions.
>
> Forest Wilson
> Cherokee Fire
>
> Sent from my Verizon Wireless Phone
>
> ----- Reply message -----
> From: "Pielow, Robert" <[email protected]>
> Date: Tue, Apr 13, 2010 5:32 PM
> Subject: Pipe Wrapping
> To: "[email protected]" <[email protected] 
> >
>
> That might come as a surprise to those who have paid UL for testing  
> and listing under VGNJ.GuideInfo
> Heating Cable Systems for Use on Fire Protection System Piping
>
> Robert J. Pielow, P.E.
> Fire Protection & Life Safety
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected] 
> ] On Behalf Of [email protected]
> Sent: Tuesday, April 13, 2010 4:27 PM
> To: [email protected]
> Subject: Re: Pipe Wrapping
>
> There is no listed heat trace system for fire sprinkler systems.
>
> Forest Wilson
> Cherokee Fire
>
> Sent from my Verizon Wireless Phone
>
> ----- Reply message -----
> From: "John Denhardt" <[email protected]>
> Date: Tue, Apr 13, 2010 11:18 AM
> Subject: Pipe Wrapping
> To: <[email protected]>
>
> You can wrap it with insulation but the real question is why.  If you
> are using it with a listed heat trace system for sprinkler piping than
> MAYBE I understand.
>
> John
>
> John August Denhardt, P.E.
> Strickland Fire Protection Incorporated
> 5113 Berwyn Road
> College Park, Maryland 20740
> Office Telephone Number:  301-474-1136
> Mobile Telephone Number:  301-343-1457
> FIRE SPRINKLERS SAVE LIVES
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Roland
> Huggins
> Sent: Tuesday, April 13, 2010 11:32 AM
> To: [email protected]
> Subject: Re: Pipe Wrapping
>
> and even that restriction has changed
>
> Roland
>
> On Apr 13, 2010, at 8:26 AM, Don Lowry wrote:
>
>> I believe you may talking about (2002) and probably others (Not 2010)
>> 8.15.3.1.3 and annex it is unacceptable practice to heat trace and
>> insulate
>> branchlines.
>>
>> Don
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to