Sprinklers are not required if it meets all requirements of NFPA 2002, section 8.14.6.2.
Jack Fairchild, CFPS | Senior Fire Protection Designer | Ballinger | v 215.446.0596 | f 215.446.0597 | 833 Chestnut Street Suite 1400 Philadelphia, PA 19107 | www.ballinger-ae.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of A.P.Silva Sent: Saturday, May 15, 2010 12:41 AM To: [email protected] Subject: CC sprinklers NFPA has requirements for combustible concealed space sprinklers. However, the TYCO CC sprinklers have their own restrictions on the application. Such as, to be used for light hazard only. If used with TJI's, the TJI space has to be filled with non-combustible insulation etc. What happens if these restrictions don't apply. Use standard heads? Or use CC heads regardless, as they are required by NFPA? What I have is a 24" to 36" deep crawlspace, the ceiling of which comprises of TJI's which are exposed to the space below. The insulation is on the floor and not in the TJI space. The building is a school, but specd. To be designed for OH 1. Any comments? Also, any other manufacturer's for CC heads? Tony _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)