Perhaps, but Tyco's Raychem  "XL-Trace System for Fire Sprinkler  
Freeze Protection Design Guide and Installation Manual" certainly  
contains a lot of information about how to do branch lines and  
sprinklers. There does not seem to be a listing reference.

http://www.tycothermal.com/assets/Americas/English/Document/Design%20Guidelines/5329/H58489_XLTrace_Fire_Sprinkler_DG_0110.pdf

The local sales arm came around recently to tell us about it. It was  
so new to them that they actually knew nothing about it other than  
instructions from higher up to knock on some doors. Maybe the listing  
is forthcoming.

Allan Seidel
St. Louis, MO


On Apr 13, 2010, at 5:31 PM, Roland Huggins wrote:

> there IS listed heat tracing for sprinkler system but there are NONE
> yet listed for use on BRANCH LINES.  At least not the last time I
> checked.
>
> Roland
>
> On Apr 13, 2010, at 3:00 PM, [email protected] wrote:
>
>> Thank you for the info.
>> I just read a tech bulletin from the NFSA this morning, and I
>> thought it said they were unaware of listed trace systems.
>> This shows the importance of asking multiple sources for opinions.
>>
>> Forest Wilson
>> Cherokee Fire
>>
>> Sent from my Verizon Wireless Phone
>>
>> ----- Reply message -----
>> From: "Pielow, Robert" <[email protected]>
>> Date: Tue, Apr 13, 2010 5:32 PM
>> Subject: Pipe Wrapping
>> To: "[email protected]" <[email protected]
>>>
>>
>> That might come as a surprise to those who have paid UL for testing
>> and listing under VGNJ.GuideInfo
>> Heating Cable Systems for Use on Fire Protection System Piping
>>
>> Robert J. Pielow, P.E.
>> Fire Protection & Life Safety
>>
>>
>>
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]
>> ] On Behalf Of [email protected]
>> Sent: Tuesday, April 13, 2010 4:27 PM
>> To: [email protected]
>> Subject: Re: Pipe Wrapping
>>
>> There is no listed heat trace system for fire sprinkler systems.
>>
>> Forest Wilson
>> Cherokee Fire
>>
>> Sent from my Verizon Wireless Phone
>>
>> ----- Reply message -----
>> From: "John Denhardt" <[email protected]>
>> Date: Tue, Apr 13, 2010 11:18 AM
>> Subject: Pipe Wrapping
>> To: <[email protected]>
>>
>> You can wrap it with insulation but the real question is why.  If you
>> are using it with a listed heat trace system for sprinkler piping  
>> than
>> MAYBE I understand.
>>
>> John
>>
>> John August Denhardt, P.E.
>> Strickland Fire Protection Incorporated
>> 5113 Berwyn Road
>> College Park, Maryland 20740
>> Office Telephone Number:  301-474-1136
>> Mobile Telephone Number:  301-343-1457
>> FIRE SPRINKLERS SAVE LIVES
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Roland
>> Huggins
>> Sent: Tuesday, April 13, 2010 11:32 AM
>> To: [email protected]
>> Subject: Re: Pipe Wrapping
>>
>> and even that restriction has changed
>>
>> Roland
>>
>> On Apr 13, 2010, at 8:26 AM, Don Lowry wrote:
>>
>>> I believe you may talking about (2002) and probably others (Not  
>>> 2010)
>>> 8.15.3.1.3 and annex it is unacceptable practice to heat trace and
>>> insulate
>>> branchlines.
>>>
>>> Don
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)