I've tried to stay out of this since we seem to re-hash this every 6 months
or so.
For a RE-CAP of all our past discussion, let's start with: "It's outside of
the scope of NFPA 13"
Now your EOR didn't say comply with NFPA 13, he called for a NFPA compliant
system. So have him clarify what type of NFPA compliant system.
10,11,12,12A,14,15, 16,17 or 17A or possibly OTHER?
As a "Layout Tech." and NOT a FPE your required to follow the guidance of
the engineer. But as the EOR, he's required to provide that guidance. So
your job is to make him do his job. (Let's not go into CET/SET vs. PE)

Since no really good study, where they burn down one of these structures has
been done yet, what we don't know still exceeds what we do know. Get the
ERO, AHJ, Owner and Insurance underwriter to tell you what they can all
agree on as appropriate protection in writing, and then you can do what they
explicitly direct you to do for a layout.

Otherwise just head to the bar, and stay there until you forget all about
this project. No need to run, but you should call a taxi, as we cannot
endorse unsafe behavior.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of tom poisal
Sent: Monday, May 03, 2010 6:43 PM
To: [email protected]
Subject: Re: boat storage

okay Todd so today, what do I do?


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to