So we can't consider a ceiling a collection of interconnected 15'x 
15' heat collectors?



At 03:13 PM 5/20/2010, you wrote:
>That reference does NOT support the existence of functional heat
>collectors - even if you presume such a thing (I prefer to use assume
>since we know what that means).  It's to stop folks from sticking
>small items over the sprinkler then claiming they provide some value.
>As the Annex points out, such items more often than not slow down
>activation times.
>
>There can be a rare reason to place small horizontal items above the
>sprinkler. At the DOE plant we used 1 sq ft of metal over some of our
>sprinklers.  It was on our cooling towers over the motors and  it
>wasn't a "heat collector" but a crap deflector from the birds.  Other
>than the in-rack sprinkler assembly, I can't think of another good
>reason.
>
>Roland
>
>On May 19, 2010, at 2:36 PM, Chris Cahill wrote:
>
> > Who knows maybe it's not a change and the AHJ accepted as a heat
> > collector.
> > BTW I've been corrected heat collectors do exist.  NFPA 13 '10 says
> > so. So
> > next time someone says there is no such thing as a heat collector
> > refer them
> > to 13 '10-8.5.4.1.4 and the only limit is when used as a means to
> > assist the
> > activation of a sprinkler. So it presumes there are other legal uses
> > of heat
> > collectors. But I digress.
> >
> > Chris Cahill, P.E.
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to