Didn't realize you were from Texas since most don't consider 15' x 15'  
a SMALL item.  Even such large sections with opening between them  
(often called floating clouds) are not an acceptable ceiling but just  
an obstruction.

Roland

On May 20, 2010, at 12:16 PM, Todd Williams wrote:

> So we can't consider a ceiling a collection of interconnected 15'x
> 15' heat collectors?
>
>
>
> At 03:13 PM 5/20/2010, you wrote:
>> That reference does NOT support the existence of functional heat
>> collectors - even if you presume such a thing (I prefer to use assume
>> since we know what that means).  It's to stop folks from sticking
>> small items over the sprinkler then claiming they provide some value.
>> As the Annex points out, such items more often than not slow down
>> activation times.
>>
>> There can be a rare reason to place small horizontal items above the
>> sprinkler. At the DOE plant we used 1 sq ft of metal over some of our
>> sprinklers.  It was on our cooling towers over the motors and  it
>> wasn't a "heat collector" but a crap deflector from the birds.  Other
>> than the in-rack sprinkler assembly, I can't think of another good
>> reason.
>>
>> Roland
>>
>> On May 19, 2010, at 2:36 PM, Chris Cahill wrote:
>>
>>> Who knows maybe it's not a change and the AHJ accepted as a heat
>>> collector.
>>> BTW I've been corrected heat collectors do exist.  NFPA 13 '10 says
>>> so. So
>>> next time someone says there is no such thing as a heat collector
>>> refer them
>>> to 13 '10-8.5.4.1.4 and the only limit is when used as a means to
>>> assist the
>>> activation of a sprinkler. So it presumes there are other legal uses
>>> of heat
>>> collectors. But I digress.
>>>
>>> Chris Cahill, P.E.
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to