Any comments about the Safety Alert from NFPA concerning anti-freeze in 
residential fire sprinkler systems?

I'm not comfortable requiring these systems to be drained down, filled with 
water and no real fix in place.

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
** Note new email address: [email protected]
 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brad
Sent: Wednesday, July 07, 2010 1:06 PM
To: 'John Drucker'; [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

Thanks John it all makes sense now-- (I had not considered any horizontal
separation type concepts bcoz the project in question is one story I guess)

-----Original Message-----
From: John Drucker [mailto:[email protected]] 
Sent: Wednesday, July 07, 2010 12:46 PM
To: [email protected]; [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

Brad,

At issue is the notion of horizontal fire separation assembly being the
same as a firewalls.

There are two building separation concepts; 1) open space which allows
adjacent buildings to burn down without effecting another or 2) a fire
wall which allows adjacent buildings to burn down without effecting
another. In both cases the fire building is consumed without affecting
adjacent buildings.

Obviously distance speaks for itself. 

The concept of a firewall delineating separate buildings is founded on a
critical performance criteria ; "2006 IBC 702.1 FIRE WALL. A
fire-resistance-rated wall having protected openings, which restricts
the spread of fire and extends continuously from the foundation to or
through the roof, WITH SUFFICIENT STRUCTURAL STABILITY UNDER FIRE
CONDITIONS TO ALLOW COLLAPSE OF CONSTRUCTION ON EITHER SIDE without
collapse of the wall."

So I ask, how does a horizontal fire assembly comply with this critical
performance requirement ?.  The answer it doesn't.

But to answer your question; "if a 2-hour wall between light hazard and
something less than light hazard is called equivalent to a separate
building by the officials, then what do you rename it to?"  No need to
rename it since a 2 hour fall WALL qualifies the construction as two
separate buildings, so 13 in the non residential BUILDING and 13R is the
residential BUILDING.

John Drucker Jr CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Borough of Red Bank, NJ 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Sent: Wednesday, July 07, 2010 1:17 PM
To: 'John Drucker'; [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

John,
Good idea with the name change, but it would not satisfy those whom want
to see nothing but sky surrounding nothing but residential-- 

-----Original Message-----
From: John Drucker [mailto:[email protected]]
Sent: Wednesday, July 07, 2010 12:00 PM
To: [email protected]; [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

David,

Exactly. Where all this "hybrid" stuff came from is beyond me. If you
have a building that qualifies as NFPA-13R then the system is a 13R
System.
NFPA-13R merely refers back to certain sections of 13 as a technical
reference not to imply that the system is somehow two systems, or a
13R/13 system.

Hypothetically if 13R was a standalone standard, i.e. copying and
pasteing the needed sections of 13, there wouldn't be any confusion
since users would never venture beyond 13R. But we all know that it
would increase the cost of the standard.

One simple change would solve the mixed use conundrum;

NFPA 13R: "Standard for the Installation of Sprinkler Systems in
RESIDENTIAL Occupancies up to and Including Four Stories in Height".

To

NFPA 13R: "Standard for the Installation of Sprinkler Systems in
RESIDENTIAL BUILDINGS up to and Including Four Stories in Height". 

John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Autry,
David
Sent: Wednesday, July 07, 2010 10:23 AM
To: [email protected]; [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

I believe you can ONLY have a 13 building or a 13R building. You can't
mix
and match. One or the other.


David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
** Note new email address: [email protected]
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Sent: Wednesday, July 07, 2010 9:20 AM
To: 'Art Tiroly'; [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

Residential heads and their calc rules are great where you can use them.
You
would not be able to use them in say the physical therapy room, whether
it
was 13 OR 13R. By true occupancy separation, you eliminate a lot of
bathroom
and closet heads, AND attic sprinklers.  


-----Original Message-----
From: Art Tiroly [mailto:[email protected]] 
Sent: Wednesday, July 07, 2010 9:02 AM
To: [email protected]; [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

The Ohio IBC has allowed and encourages the use of residential
sprinklers in
"I" occupancies. We have used the residential rules in 13 with 4 head
calc
areas for many years. But attics etc are required for 100% sprinkler
coverage due to NFPA 13 requirements per IBC for the I occupancy.

ART
ATCO Fire Protection 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Sent: Wednesday, July 07, 2010 9:50 AM
To: [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

If this question is raised before the Arch finalizes the design, then
the
common "I" areas (core) can be separated from the "R" (sleeping wings)
with
a 2-hour wall, then 13 AND 13R apply, the overall cost is probably
reduced,
and there is nothing wrong from a fire protection view.

-----Original Message-----
From: Daniel Adams [mailto:[email protected]]
Sent: Tuesday, July 06, 2010 4:47 PM
To: [email protected]
Subject: Question regarding NFPA 13 vs. NFPA 13R

For a single-story *assisted living* center, can 13R be used for the
system
design ? If it can be designed per NFPA 13R, at what point would it need
to
be protected per NFPA 13 ? I realize that 13R covers residential units
up to
4 levels, but where this is an assisted living center, does this make a
difference ?

Dan Adams
Designer

Interwest Fire Protection, Inc.
404 Ironwood Drive
Salt Lake City, UT 84115

Phone:     (801) 746-4040
Fax:         (801) 746-4043
[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity
to which it is addressed and may contain information that is privileged and
confidential, nor is it, unless specifically stated, intended to be relied
upon by any person or persons other than the individual or entity named
above and no warranties or representations are made or intended to persons
or entities not named above.  If the reader is not the intended recipient,
you are hereby notified that any dissemination, distribution or copying of
this communication is strictly prohibited.  If you have received this
communication in error, please notify us immediately by telephone, return
this message to the address above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to