John,
Good idea with the name change, but it would not satisfy those whom want to
see nothing but sky surrounding nothing but residential-- if a 2-hour wall
between light hazard and something less than light hazard is called
equivalent to a separate building by the officials, then what do you rename
it to?

-----Original Message-----
From: John Drucker [mailto:[email protected]] 
Sent: Wednesday, July 07, 2010 12:00 PM
To: [email protected]; [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

David,

Exactly. Where all this "hybrid" stuff came from is beyond me. If you have a
building that qualifies as NFPA-13R then the system is a 13R System.
NFPA-13R merely refers back to certain sections of 13 as a technical
reference not to imply that the system is somehow two systems, or a 13R/13
system.

Hypothetically if 13R was a standalone standard, i.e. copying and pasteing
the needed sections of 13, there wouldn't be any confusion since users would
never venture beyond 13R. But we all know that it would increase the cost of
the standard.

One simple change would solve the mixed use conundrum;

NFPA 13R: "Standard for the Installation of Sprinkler Systems in RESIDENTIAL
Occupancies up to and Including Four Stories in Height".

To

NFPA 13R: "Standard for the Installation of Sprinkler Systems in RESIDENTIAL
BUILDINGS up to and Including Four Stories in Height". 

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Autry, David
Sent: Wednesday, July 07, 2010 10:23 AM
To: [email protected]; [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

I believe you can ONLY have a 13 building or a 13R building. You can't mix
and match. One or the other.


David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
** Note new email address: [email protected]
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Sent: Wednesday, July 07, 2010 9:20 AM
To: 'Art Tiroly'; [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

Residential heads and their calc rules are great where you can use them. You
would not be able to use them in say the physical therapy room, whether it
was 13 OR 13R. By true occupancy separation, you eliminate a lot of bathroom
and closet heads, AND attic sprinklers.  


-----Original Message-----
From: Art Tiroly [mailto:[email protected]] 
Sent: Wednesday, July 07, 2010 9:02 AM
To: [email protected]; [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

The Ohio IBC has allowed and encourages the use of residential sprinklers in
"I" occupancies. We have used the residential rules in 13 with 4 head calc
areas for many years. But attics etc are required for 100% sprinkler
coverage due to NFPA 13 requirements per IBC for the I occupancy.

ART
ATCO Fire Protection 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Sent: Wednesday, July 07, 2010 9:50 AM
To: [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

If this question is raised before the Arch finalizes the design, then the
common "I" areas (core) can be separated from the "R" (sleeping wings) with
a 2-hour wall, then 13 AND 13R apply, the overall cost is probably reduced,
and there is nothing wrong from a fire protection view.

-----Original Message-----
From: Daniel Adams [mailto:[email protected]]
Sent: Tuesday, July 06, 2010 4:47 PM
To: [email protected]
Subject: Question regarding NFPA 13 vs. NFPA 13R

For a single-story *assisted living* center, can 13R be used for the system
design ? If it can be designed per NFPA 13R, at what point would it need to
be protected per NFPA 13 ? I realize that 13R covers residential units up to
4 levels, but where this is an assisted living center, does this make a
difference ?

Dan Adams
Designer

Interwest Fire Protection, Inc.
404 Ironwood Drive
Salt Lake City, UT 84115

Phone:     (801) 746-4040
Fax:         (801) 746-4043
[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to