Chris,
Back to this one boys and girls.
I respectfully disagree.
NFPA 13, 2010 states, "An antifreeze solution shall be prepared with a
freezing point below the expected minimum temperature for the locality."

I'm not sure why you wouldn't use the record low to be safe.  A strong
wind can lower temperatures in attics and concealed spaces quickly.

As the EOR or the designer I really don't think it is worth chancing
temperature and wind combinations (and don't get someone started on
wind-chill - I'm using wind to indicate that it can cool an area [attic
or concealed space] quicker if the wind is blowing in through holes,
seams, missing or misplaced insulation, and so on) and not planning for
conceivable low temperatures in the modern era.  Minneapolis record low
for February (2nd) 1996 is -32, -27 in December 1996, January is -32 in
1977, -34 in 1970 according to the National Weather Service.

I don't see 50/50 Glycerin or PG appropriate for most of Minnesota, part
of Iowa, most of 'Nort' Dakota, or Wisconsin....

Scott Futrell
 
(763) 425-1001 Office
(612) 759-5556 Cell
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Friday, July 09, 2010 1:04 PM
To: [email protected]
Subject: Re: Anti-Freeze

I believe 50/50 is still fine.  I believe we are to use the average mean
low temp (or something like that if I got the name wrong) not the all
time record.  Around here record is -36 mean low is -25.  Sornsin's are
may be a couple lower. 

Second the reported temps are the first ice crystals not the burst temp
where things break. Burst is about 20 lower.  Try it in your kitchen
with dry ice. And yes I have.  Now at reported temps its like a milk
shake and won't flow well but will eventually clear.

And C just because the air temp is what ever the AF won't be.  Record
lows are for a short time.  Factor in thermal lag, internal convection
currents and the location of the piping (like in a slightly warmer
attic) and most of the US including most of SD, MN an MA will be fine
with 50/50.

Chris Cahill
Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "George Church" <[email protected]>
Sender: [email protected]
Date: Fri, 9 Jul 2010 12:24:38 
To: <[email protected]>
Reply-To: [email protected]
Subject: RE: Anti-Freeze

Gregg, I believe the TC members have a week to chaneg their minds after
reading the other memeber's comments in the initial vote, so I don;t
think
anything is cast in stone except Chris stating NFPA recommends leaving
em
wet for now- and assuming, i'm sure, that before freezing weather, there
will be a larger knowledge base and a direction in which to run.

potential TIAs were either a ban or a requirement to use premix 50-50.
Guess
global warming better head toward the Sornsin boys cause i'll bet 50-50
doesn't meet their needs at -35.

glc 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Gregg
Fontes
Sent: Friday, July 09, 2010 12:05 PM
To: [email protected]
Subject: RE: Anti-Freeze

I have reviewed the July 2010 TIA, so if you have a system that is in
design
as we speak, if you use a 50% or less factory premixed solution, it is
acceptable?  The revised TIA, I think states that it is?  

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Friday, July 09, 2010 8:53 AM
To: [email protected]
Subject: Re: Anti-Freeze

Below is the AFSA Alert to our members.

Additional testing is underway.  The NFPA and Fire Protection Research
Foundation with the support of the sprinkler industry are moving
incredibly
fast.  There was a NFPA 13 TCC meeting on this subject earlier this year
and
the initial fire testing was completed in a few months indicating that a
threat exists and that it appears to be restricted to a narrow scenario
in
he kitchen.  A second round of more detailed testing has been launched
to
determine definitively whether other locations may display similar
consequences and what levels of concentrations are safe to be used.
These
tests are underway and will also be completed in an amazingly short
period
of time (doing things in weeks instead of many months/years).

Since the Truckee fire has been mentioned, I'd like to say proceed with
cation.  The Fire Department report says there is not enough information
yet
to draw any conclusions and the other report casually jumps to a broad
conclusion.  There are some very interesting explosion patterns that
should
have been addressed as part of that conclusion.

Roland


AFSA Member
Alert 
 
July
  7, 2010



NFPA issues safety alert regarding antifreeze in residential sprinklers
On July 6, the National Fire Protection Association (NFPA) issued a  
safety alert recommending that residential fire sprinkler systems  
containing antifreeze should be drained and the antifreeze replaced  
with water. The alert follows a research study and an initial set of  
fire tests conducted after a fire incident raised concerns about  
antifreeze solutions in residential sprinkler systems. The incident  
involved a grease fire in a kitchen where a sprinkler with a high  
concentration of antifreeze deployed. The fire resulted in a single  
fatality and serious injury to another person.

AFSA has been and continues to follow these developments closely. We  
have urged that testing be conducted as quickly as possible, with the  
hope that the results and subsequent standards modifications can be  
made before cold weather arrives. AFSA is mindful that NFPA is  
obligated to take strong positions in support of life safety and we  
anticipated a moratorium on the use of antifreeze until testing was  
complete, but we were surprised by the recommendation to drain  
existing systems and replace antifreeze with water.

NFPA and the NFPA Research Foundation have put this issue as a top  
priority. They are moving very rapidly to complete testing on this  
issue. NFPA anticipates that testing will be complete, and Tentative  
Interim Amendments (TIAs) will be addressed prior to the Standards  
Council meeting in August. Their goal is to have recommendations or  
standards modifications prior to the arrival of the "cold season."

AFSA will continue to work closely with NFPA and keep you informed on  
future developments. Expect to hear more soon. Complete information is  
available from NFPA at www.nfpa.org/antifreeze/.


On Jul 7, 2010, at 11:25 AM, Autry, David wrote:

> Any comments about the Safety Alert from NFPA concerning anti-freeze  
> in residential fire sprinkler systems?
>
> I'm not comfortable requiring these systems to be drained down,  
> filled with water and no real fix in place.
>
> David Autry
> Plans Examiner
> Nebraska State Fire Marshal's Office

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to