Simultaneous fires in an industrial building and/or warehouse, plus in an airport hanger could add up to a large demand. Or even two hangers. Any domestic or other draw off this system besides fire? What you are trying to design is similar to a municipal water system and those demand would be large compared to what we usually deal with.


At 06:46 AM 9/20/2010, you wrote:
Fire water mains of a propritary large development shall serve multiple sprinklered buildings spaced well apart. Envision an industrial plant, an airport or a university campus including laboratories. The fire water mains shall also serve fire brigade hydrants.

In such cases we comply with a number of standards within NFPA (such as 1, 13, 24, 14, 101 and the occupancy specific standards) or similar. Add to this national regulations. Add to this hose allowance. Even add to this stakeholder demand to cope with two simultaneous fires.

In complying to all requirements, water demand tends to increase by method of addition to seemingly unrealistic proportion. Each standard incorporate a kind of safety factor, so in lack of a systematic approach (like probability risk analysis) water demand is unduly increased.

Any suggestion to a guide or a standard that addresses this?
Any experience on determining the demand at such large proprietary fire water mains?

I am not asking about the water mains design. My concern is assessment of water demand only.


Geir Jensen
COWI Fire
Technical Director
[email protected]<mailto:%[email protected]>
www.cowi.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to