Why in God's name does he want (or anyone) want sprinklers in an oven, no matter how big? I once had to put sprinklers in a building over a molten salt bath (1000 degrees F). The manufacturer's literature said not too (for obvious explosive reasons) so to separate the potential deaths from the life safety equipment we built a $22,000 hood over the salt bath leaving about a three foot perimeter between the hood and the building walls. The salt bath was the only thing in the building.
On Wed, Nov 17, 2010 at 11:02 AM, <[email protected]> wrote: > No don't use a wet drop. Use a dry sprinkler. Had to do this several years > ago. The mfgr told us they could provide the 650deg head on the dry barrel > but it wouldn't be UL listed. Need to check if that's an issue or not with > AHJ. > > Craig L. Prahl, CET > Fire Protection > CH2MHILL > Lockwood Greene > 1500 International Drive > Spartanburg, SC 29304-0491 > Direct - 864.599.4102 > Fax - 864.599.8439 > CH2MHILL Extension 74102 > [email protected] > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Mark.Phelps > Sent: Wednesday, November 17, 2010 2:00 PM > To: [email protected] > Subject: RE: Industrial Ovens - 500 degrees > > Ask the AHJ if he wants the system to be wet, or dry? Then think about what > happens to water at 212 degrees. > Mark at Aero > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Greg McGahan > Sent: Wednesday, November 17, 2010 8:48 AM > To: [email protected] > Subject: Industrial Ovens - 500 degrees > > The Local AHJ is requiring sprinklers in some Industrial Walk In ovens - > the largest of which is 12' x 20' - BUT the highest expected temperature > is 500 degree in the space and the highest temp sprinklers I am aware of > are 500 degrees. > > Ideas? > Thanks, > Greg >> >> > > -- > Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road > Cantonment, FL 32533 850-937-1850 Fax 850-937-1852 > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)