What's the question?  If there are no walls extending to the ceiling/roof 
wouldn't you just install the sprinklers at the underside of the deck?  Use OH1 
criteria over the spaces and 15 ft beyond the low walls. Is this a big open are 
or are there other walls or ???????????   More info would be helpful.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, March 10, 2011 10:22 AM
To: [email protected]
Subject: partial walls in mech rooms

We have an issue right now with a light hazard non-combustible building in
which there are multiple small mechanical rooms -3' x 8' or 6' x 7' in
general size. The architect was vague so the GC is not putting in ceilings
nor is he running the walls up to the deck.

I have been reading and rereading chapter 8 of 13 -2010 edition, and I
cannot conclusively determine what we are required to do in this case. The
description in 8.15.22.1 is not exactly correct so I can't see clearly...

Does anybody have a cut and dry answer?
Thanks,
Greg

-- 
Greg McGahan
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to