Mike-
What section references the 24' ?

Brian Harris
FDFP Inc.
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Morey, Mike
Sent: Thursday, March 10, 2011 10:48 AM
To: [email protected]
Subject: RE: partial walls in mech rooms

On second reading, if you're saying the LH areas have a ceiling but the
mechanical rooms don't then 8.15.22 does apply, in which case the higher
area is the roof deck, which means you provide the protection for the
mechanical room at the deck and for 24' in any direction away from the
mechanical room over the ceiling of the LH space.
 
-Mike Morey, SET
Sprinkler Designer
BMW Constructors, Inc.
office: 317-651-0596
mobile: 317-439-2695

________________________________

From: [email protected] on behalf of Greg McGahan
Sent: Thu 3/10/2011 10:21 AM
To: [email protected]
Subject: partial walls in mech rooms



We have an issue right now with a light hazard non-combustible building in
which there are multiple small mechanical rooms -3' x 8' or 6' x 7' in
general size. The architect was vague so the GC is not putting in ceilings
nor is he running the walls up to the deck.

I have been reading and rereading chapter 8 of 13 -2010 edition, and I
cannot conclusively determine what we are required to do in this case. The
description in 8.15.22.1 is not exactly correct so I can't see clearly...

Does anybody have a cut and dry answer?
Thanks,
Greg

--
Greg McGahan
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16950)
http://www.pctools.com/
=======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16950)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to