Mike- What section references the 24' ? Brian Harris FDFP Inc. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Morey, Mike Sent: Thursday, March 10, 2011 10:48 AM To: [email protected] Subject: RE: partial walls in mech rooms
On second reading, if you're saying the LH areas have a ceiling but the mechanical rooms don't then 8.15.22 does apply, in which case the higher area is the roof deck, which means you provide the protection for the mechanical room at the deck and for 24' in any direction away from the mechanical room over the ceiling of the LH space. -Mike Morey, SET Sprinkler Designer BMW Constructors, Inc. office: 317-651-0596 mobile: 317-439-2695 ________________________________ From: [email protected] on behalf of Greg McGahan Sent: Thu 3/10/2011 10:21 AM To: [email protected] Subject: partial walls in mech rooms We have an issue right now with a light hazard non-combustible building in which there are multiple small mechanical rooms -3' x 8' or 6' x 7' in general size. The architect was vague so the GC is not putting in ceilings nor is he running the walls up to the deck. I have been reading and rereading chapter 8 of 13 -2010 edition, and I cannot conclusively determine what we are required to do in this case. The description in 8.15.22.1 is not exactly correct so I can't see clearly... Does anybody have a cut and dry answer? Thanks, Greg -- Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16950) http://www.pctools.com/ ======= ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16950) http://www.pctools.com/ ======= _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)