Seems like 11.1.2 (2010 13) would address your situation adequately, paraphrased: areas not seperated physically must have the greater demand extended 15' beyond the perimiter of the higher hazard area. -Mike Morey, SET Sprinkler Designer BMW Constructors, Inc. office: 317-651-0596 mobile: 317-439-2695
________________________________ From: [email protected] on behalf of Greg McGahan Sent: Thu 3/10/2011 10:21 AM To: [email protected] Subject: partial walls in mech rooms We have an issue right now with a light hazard non-combustible building in which there are multiple small mechanical rooms -3' x 8' or 6' x 7' in general size. The architect was vague so the GC is not putting in ceilings nor is he running the walls up to the deck. I have been reading and rereading chapter 8 of 13 -2010 edition, and I cannot conclusively determine what we are required to do in this case. The description in 8.15.22.1 is not exactly correct so I can't see clearly... Does anybody have a cut and dry answer? Thanks, Greg -- Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)