Seems like 11.1.2 (2010 13) would address your situation adequately, 
paraphrased: areas not seperated physically must have the greater demand 
extended 15' beyond the perimiter of the higher hazard area.
 
-Mike Morey, SET
Sprinkler Designer
BMW Constructors, Inc.
office: 317-651-0596
mobile: 317-439-2695

________________________________

From: [email protected] on behalf of Greg McGahan
Sent: Thu 3/10/2011 10:21 AM
To: [email protected]
Subject: partial walls in mech rooms



We have an issue right now with a light hazard non-combustible building in
which there are multiple small mechanical rooms -3' x 8' or 6' x 7' in
general size. The architect was vague so the GC is not putting in ceilings
nor is he running the walls up to the deck.

I have been reading and rereading chapter 8 of 13 -2010 edition, and I
cannot conclusively determine what we are required to do in this case. The
description in 8.15.22.1 is not exactly correct so I can't see clearly...

Does anybody have a cut and dry answer?
Thanks,
Greg

--
Greg McGahan
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to