>From 24 to 42 square feet of floor (the floor is where we design for the
fire starting)-- does this floor space require a thousand or two square feet
of sprinklers?
 
-----Original Message-----
From: Matthew J. Willis [mailto:[email protected]] 
Sent: Thursday, March 10, 2011 10:17 AM
To: [email protected]
Subject: RE: partial walls in mech rooms

?

 

 

Matthew J. Willis
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of Brad Casterline
> >Sent: Thursday, March 10, 2011 10:10 AM
> >To: [email protected]
> >Subject: RE: partial walls in mech rooms
> >
> >I cannot get past the idea that we normally put water on floors, not on
> >the
> >tops of ceilings!
> >
> >-----Original Message-----
> >From: Greg McGahan [mailto:[email protected]]
> >Sent: Thursday, March 10, 2011 10:00 AM
> >To: [email protected]
> >Subject: Re: partial walls in mech rooms
> >
> >It is not CLEAR, this section appears to refer to the "cloud" situation
> >we
> >are often running into.
> >
> >I am not trying to get out of something here, I am trying to document why
> >we
> >have to do it. We have used the 15' rule in the past, but again, that is
> >truly intended for another situation, in my honest opinion. This section
> >is
> >to avoid fusing heads in adjacent areas, not require additional
> >protection... as I read it.
> >
> >On Thu, Mar 10, 2011 at 9:47 AM, Morey, Mike <[email protected]> wrote:
> >
> >> On second reading, if you're saying the LH areas have a ceiling but the
> >> mechanical rooms don't then 8.15.22 does apply, in which case the
> >higher
> >> area is the roof deck, which means you provide the protection for the
> >> mechanical room at the deck and for 24' in any direction away from the
> >> mechanical room over the ceiling of the LH space.
> >>
> >> -Mike Morey, SET
> >> Sprinkler Designer
> >> BMW Constructors, Inc.
> >> office: 317-651-0596
> >> mobile: 317-439-2695
> >>
> >> ________________________________
> >>
> >> From: [email protected] on behalf of Greg
> >McGahan
> >> Sent: Thu 3/10/2011 10:21 AM
> >> To: [email protected]
> >> Subject: partial walls in mech rooms
> >>
> >>
> >>
> >> We have an issue right now with a light hazard non-combustible building
> >in
> >> which there are multiple small mechanical rooms -3' x 8' or 6' x 7' in
> >> general size. The architect was vague so the GC is not putting in
> >ceilings
> >> nor is he running the walls up to the deck.
> >>
> >> I have been reading and rereading chapter 8 of 13 -2010 edition, and I
> >> cannot conclusively determine what we are required to do in this case.
> >The
> >> description in 8.15.22.1 is not exactly correct so I can't see
> >clearly...
> >>
> >> Does anybody have a cut and dry answer?
> >> Thanks,
> >> Greg
> >>
> >> --
> >> Greg McGahan
> >> Living Water Fire Protection, LLC
> >> 1160 McKenzie Road
> >> Cantonment, FL 32533
> >> 850-937-1850
> >> fax 850-937-1852
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >> (Put the word unsubscribe in the subject field)
> >>
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >> (Put the word unsubscribe in the subject field)
> >>
> >
> >
> >
> >--
> >Greg McGahan
> >Living Water Fire Protection, LLC
> >1160 McKenzie Road
> >Cantonment, FL 32533
> >850-937-1850
> >fax 850-937-1852
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >No virus found in this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.872 / Virus Database: 271.1.1/3493 - Release Date: 03/10/11
> >01:34:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to