I have to second George's response.  Having an AOR or EOR or AHJ tell you
it's OK to design a sprinkler system that doesn't meet applicable standards
(NFPA 13 in this case) doesn't shield you from liability if something goes
wrong.  As a sprinkler contractor, you're generally not considered a code
expert.  But any plaintiff lawyer worth his salt will successfully paint you
as a sprinkler expert.  As a sprinkler expert, you should have know to
design for 3000 sf.

OK, back to my regularly scheduled day job. 

Ed "J Cochran" Kramer



> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of George Church
> Sent: Wednesday, June 22, 2011 10:20 AM
> To: [email protected]
> Subject: RE: Building trade off update
> 
> Only one question- was the mtg documented so you have a copy to take to
> court in 2014?
> 
> 
> George L.  Church, Jr., CET
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
> 
> 
> 
> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of Rod DiBona
> Sent: Wednesday, June 22, 2011 11:05 AM
> To: [email protected]
> Subject: Building trade off update
> 
> 
> I wanted to follow up and let everyone who helped me think through the
> process know what happened. This was a new two story courthouse (A3)
> with a combustible attic above the 2nd floor and a single (B) occupancy
> attached adjacent on the ground floor.  IBC 2009. He was sprinklering
> the basement, 1st and 2nd but not the attic. We met with the Architect
> and and asked him if he could educate us on his decision tree that
> allowed:
> 
> 
>  1.   No sprinklers in the combustible attic that was draft stopped
> every 3,000 ft.
>  2.   Install fire protection on the first and second floors (not
> required systems in the A3) to allow a reduction in fire rating of the
> corridor walls, stairs, and the wall separating the courtroom A3 from
> the B occupancy.
>  3.  His logic for not mandating an increase of the design area on the
> 2nd floor to 3,000 ft.
> 
> His answers were:
> 
> 
>  1.  The IBC 2009 doesn't require sprinklers  except for the basement,
> so NFPA 13 isn't applicable.
>  2.  He stated that the IBC allows for reduction with partial systems.
> 901.2 "exception"
>  3.  He believed that because partial systems are allowed and that
> because the code didn't require a system in the attic that we wouldn't
> need to increase our area on the 2nd floor even though the combustible
> attic above was unsprinklered.
> 
> We took the advice of GC / Roland and others and listened and accepted
> what he said. The tone of the meeting was very good and at the end of
> the day I am glad he chose more sprinklers than required in lieu of more
> rating. I personally don't agree with the lack of increase in area (
> question #3) but as it has been pointed out...... not my decision.
> 
> Thanks for all the input and help. We learn and move on.
> 
> 
> Rod DiBona
> Rapid Fire Protection
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to