Have a variance hearing end of month, helpful- TX!

George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, June 22, 2011 5:58 PM
To: [email protected]
Subject: RE: Building trade off update

Careful on variations, you still may be on the hook.

Here's NJ's construction code regulation on the matter.

N.J.A.C. 5:23-2.9   Variations and exceptions -
  
(a) No variations or exceptions from the requirements of any subcode of these 
regulations may be made, EXCEPT UPON THE FOLLOWING FINDINGS:

1. That strict compliance with any specific subcode provision, if required, 
would result in PRACTICAL DIFFICULTY to such owner; and
  
2. That the exception, if granted, WILL NOT JEOPARDIZE THE HEALTH, SAFETY AND 
WELFARE OF INTENDED OCCUPANTS AND THE PUBLIC GENERALLY.
  

John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or otherwise.  
Obtain required applications, permits, inspections and approvals from 
Authority(s) Having Jurisdiction. 







-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom
Sent: Wednesday, June 22, 2011 5:48 PM
To: [email protected]
Subject: RE: Building trade off update


If the AHJ won't give a written "exception or variance from code, If the Arch. 
Won't provide indemnafacation and hold harmless, if the EOR won't provide the 
same, or if the GC, PM or DB contractor won't indemnify and hold you harmless, 
your pockets are the one's hanging out there. How deep or shallow they are 
depend on your coverage and net worth.

There's many reasons NFPA 13 is a "MINIMUM" and not "All that required".

If your risk averse, you've gotten into the wrong trade. Having said that, 
there's never a good reason to multiply that risk, for the financial gain of 
others. 

Leaving protection out doesn't benefit you the contractor.
Reduced area/density designs (3000sfvs1500sf or less) at bid, doesn't translate 
into profit.
If your risk increases, so should your price. (Reduce my risk, I'll reduce your 
price.)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to