IMHO, uprights are most definitely required.   As someone else said, you
might not need to put sprinklers actually in the panels, presuming you
can meet provisions for alleviating obstruction, but you definitely need
a full complement at the deck.   Because of the economy and massive bond
measures up and down the state of CA, we do a LOT of schools work and
the trend in schools and community colleges is to employ all manner of
cloud ceiling elements, acoustic panels suspended below decks, and on
one current project we also have art panels.  Consensus solution for
some time has been to sprinkler the space above such obstructions in its
entirety ... 


Steve L.




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby
Gillett
Sent: Tuesday, October 11, 2011 6:40 AM
To: [email protected]
Subject: Architectural Panels

We have an area with Architectural Panels (aluminum) hanging from the
ceiling at 12'-0 above finish floor; the building is concrete deck on
I-beam
construction w/the top of steel at 17'-4. The panels vary in length and
width - most of them are 3'-0 wide and less with length ranging from
8'-0
and less. There are two rows of them hung together with soffit going
around
the perimeter of the area; there is a 1'-0 space between them in all
directions including between them and the soffit. The bottom of the
soffit
is even with the panels (12'-0 AFF) the architectural plan is saying it
is
40% open. The engineer wants the pipe hung above the panels and has
chrome
pendent's coming down in the 1'-0 spaces between the panels with the
deflector just below the panel (approx. 11'-11) and is saying uprights
are
not required.

 

Wouldn't uprights still be required above the panels? Wouldn't the
pendent's
need to be in the architectural panels, not in the 1'-0 open space
between
them?

 

Thank you,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <http://www.keyfireprotection.com> www.keyfireprotection.com

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20111011/7051805e/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to