We have an area with Architectural Panels (aluminum) hanging from the
ceiling at 12'-0 above finish floor; the building is concrete deck on I-beam
construction w/the top of steel at 17'-4. The panels vary in length and
width - most of them are 3'-0 wide and less with length ranging from 8'-0
and less. There are two rows of them hung together with soffit going around
the perimeter of the area; there is a 1'-0 space between them in all
directions including between them and the soffit. The bottom of the soffit
is even with the panels (12'-0 AFF) the architectural plan is saying it is
40% open. The engineer wants the pipe hung above the panels and has chrome
pendent's coming down in the 1'-0 spaces between the panels with the
deflector just below the panel (approx. 11'-11) and is saying uprights are
not required.

 

Wouldn't uprights still be required above the panels? Wouldn't the pendent's
need to be in the architectural panels, not in the 1'-0 open space between
them?

 

Thank you,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <http://www.keyfireprotection.com> www.keyfireprotection.com

 

 

 