Perfect John. I'm glad I didn't have time to look it up earlier. I'd have
bungled an explanation whereas yours was simple and elegant.

On Tue, Oct 11, 2011 at 7:18 PM, John Drucker <[email protected]>wrote:

> More Facts..................Oh Boy......
>
> Grounding is covered in NEC Article 250 Part II,III and IV,  Bonding is
> covered in NEC Article 250 Part V.  Fire Sprinkler piping is not listed in
> Article 250 as a permissible grounding electrode but is required to be
> bonded.
>
> 2008 NFPA-70 (NEC)
>
> Article 100
>
> Bonded (Bonding). Connected to establish electrical continuity and
> conductivity.
>
> Grounded (Grounding). Connected (connecting) to ground or to a conductive
> body that extends the ground connection.
>
> 2008 NFPA-70 (NEC)
>
> 250.90 General. Bonding shall be provided where necessary to ensure
> electrical continuity and the capacity to conduct safely any fault current
> likely to be imposed.
>
> 250.104 Bonding of Piping Systems and Exposed Structural Steel.
>
> (B) Other Metal Piping. "Where installed in or attached to a building or
> structure, a metal piping system(s), including gas piping, that is likely
> to
> become energized shall be bonded to the service equipment enclosure, the
> grounded conductor at the service, the grounding electrode conductor where
> of sufficient size, or the one or more grounding electrodes used. The
> bonding jumper(s) shall be sized in accordance with 250.122, using the
> rating of the circuit that is likely to energize the piping system(s). The
> equipment grounding conductor for the circuit that is likely to energize
> the
> piping shall be permitted to serve as the bonding means. The points of
> attachment of the bonding jumper(s) shall be accessible."
>
> In a nutshell the idea is to provide a low impedance path back to the power
> source in order that sufficient fault current will flow to open the
> overcurrent device preventing metallic components from staying energized.
> The key is low impedance (less resistance) path, bonding does that.
>
> So here we go....
>
> 1) 277V lighting circuit makes contact with an unbonded sprinkler pipe. No
> current flows on the sprinkler pipe because the circuit is incomplete back
> to the electrical service. The pipe is now energized at 277V. Joe the
> fitter
> comes along makes contact with the pipe and an electrical conduit which is
> bonded and completes the circuit. However the human body is a high
> impendence path, appx 2,100 ohms @ 277 Volts, so I=E/R = 277V/2,100
> Ohms=.131 Amps or 131 Milliamps, double what is need for ventricular
> fibrillation. Enough to disrupt the heart but insufficient to trip the 20
> Amp circuit breaker. The victim is electrocuted. Joe sure was a good
> fitter.
>
> 2) 277V lighting circuit makes contact with a bonded sprinkler pipe.
> Current
> flows because the circuit is complete back to the electrical service via
> the
> bonding jumper. This is a low impendence path, appx. 2 ohms (1000 ft of #12
> Copper) @ 277 volts, so I=E/R = 277V/2 Ohms= 138.5.9 Amps. The 20 Amp
> circuit breaker instantly opens and the pipe is deenergized. Hey what
> happened to the lights, Jimmy go get a flashlight, better yet coffee.
>
> Sure hope that helps,
>
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
> Fire Marshals Office
> Borough of Red Bank, NJ
>
> Not the official position of any agency, association, committee or
> otherwise.  Obtain required applications, permits, inspections and
> approvals
> from Authority(s) Having Jurisdiction.
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve
> Leyton
> Sent: Tuesday, October 11, 2011 5:59 PM
> To: [email protected]
> Subject: Grounding
>
> Assuming it's in there somewhere, where does 13 and or 24 speak to
> attaching bonding or grounding wires to sprinkler systems?   Question
> posed to me today and I had to admit that I don't know ...  hate it when
> that happens.
>
>
>
> Steve Leyton
>
> PROTECTION DESIGN & CONSULTING
>
> 2851 Camino del Rio South, Suite 400
>
> San Diego, CA 92108
>
> -------------------------------------------------------------
>
> Ph:      858.751.2930 - ext. 102
>
> Fax:    858.751.2933
>
> Cell:  619.972.5696
>
>
>
>
>
>
>
>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
> s/20111011/20e3d0e9/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111011/3f98e9bf/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to