2010:
10.6.8*   In no case shall the underground piping be used as a grounding 
electrode for electrical systems. 
10.6.8.1*   The requirement of 10.6.8 shall not preclude the bonding of the 
underground piping to the lightning protection grounding system as required by 
NFPA 780 in those cases where lightning protection is provided for the 
structure. 

Scott Futrell
 
(763) 425-1001 Office
(612) 759-5556 Cell


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Tuesday, October 11, 2011 4:59 PM
To: [email protected]
Subject: Grounding

Assuming it's in there somewhere, where does 13 and or 24 speak to
attaching bonding or grounding wires to sprinkler systems?   Question
posed to me today and I had to admit that I don't know ...  hate it when
that happens.

 