Hi Justin,

Q- Would you say that for the most part this is not a problem with sprinkler
systems since it is all metal piping which usually runs to an underground
system (ground)?

A- No. Earth is a poor (high impendence) fault path, often around 25 ohms or
worse. Using the previous example of a 277 volt lighting circuit on a 20 amp
circuit breaker and the formula, I=E/R = 277(E)/25(R)= 11.08 Amps, not
enough to trip a 20 amp circuit breaker and clear the fault. 

Ever seen a utility wire arcing in trees, on the ground or roadway ?,
notwithstanding utility companies that have replaced fuses with solids,
there's simply not enough current flowing through the earth back to the
source to open the fuse.

Q- Are there any fittings that people can think of that would break
continuity?

A- As previously stated earth is a poor fault current path. This is why a
properly sized (low impedance) bonding connection from the buildings
electrical system to metallic sprinkler piping is required. But to answer
the question Dielectric Fittings and Backflow Preventers that are removed
for service are examples of items that disrupt continuity. 

Heres a common item in most homes; the bonding jumper on a water heater. The
bonding jumper maintains continuity and thus equipotential (zero) between
hot and cold water piping. If it were missing and the hot metallic water
piping (unbonded) becomes energized and you touch both the hot and cold
valves simultaneously and the cold water piping is bonded you complete the
circuit. Better the bonding does it than the human body.

Hope that helps,

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or
otherwise.  Obtain required applications, permits, inspections and approvals
from Authority(s) Having Jurisdiction. 


 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Justin Reid
Sent: Wednesday, October 12, 2011 8:28 AM
To: [email protected]
Subject: Re: Grounding

John,

Thanks for that info, I have not looked at this issue in the past.

Would you say that for the most part this is not a problem with sprinkler
systems since it is all metal piping which usually runs to an underground
system (ground)? Are there any fittings that people can think of that would
break continuity?

Justin Reid

On Wed, Oct 12, 2011 at 12:27 AM, John Drucker
<[email protected]>wrote:

> Hmmmm. Better take a good look at the grass on your side first
> John Drucker - Mobile Email
>
> ----- Original Message -----
> From: [email protected] <
> [email protected]>
> To: [email protected] <[email protected]>
> Sent: Tue Oct 11 19:40:27 2011
> Subject: RE: Grounding
>
> Thanks all - we got this one covered.   Seems that a unified school
> district here in San Diego County had a paranoid operations manager some
> time back who required that lightning strike protection be retrofitted
> on ALL schools in the district.   Those equipped with sprinklers got
> bonded ...   never mind that we haven't had a building struck by
> lightning here in, I dunno like, FOREVER.   I guess he came from
> Oklahoma or someplace where it's an issue.
>
> If I were to be reincarnated, I hope it will be as a public employee.
> That way, I could go on drunken spending sprees with money that I don't
> really have to account for and buy stuff that I don't really need.
> That would be fun.
>
> SML
>
> No offense intended to the diligent public employees who subscribe to
> this forum, of course.   :-)
>
>
>
>  -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Roland
> Huggins
> Sent: Tuesday, October 11, 2011 3:25 PM
> To: [email protected]
> Subject: Re: Grounding
>
> 13: 10.6.8*In no case shall the underground piping be used as a
> grounding electrode for elec-
> trical systems.
>
> A.10.6.8.1While the use of the underground fire protection piping as
> the grounding elec-
> trode for the building is prohibited, NFPA 70requires that all
> metallic piping systems be
> bonded and grounded to disperse stray electrical currents. Therefore,
> the fire protection piping
> will be bonded to other metallic systems and grounded,but the
> electrical system will need
> an additional ground for its operation.
>
>
> Bonding is being connected to the ground system.  The sprinkler system
> (specified for the underground portion) can not be used as a ground
> system.  The last time I looked (more than a few days now) NEC said
> that all metal piping capable of becoming energized shall be
> grounded.  That typically is interpreted as ALL.  Must confess I
> haven't dug through the nasty details since it hasn't been a common
> problem.
>
> Roland
>
>
> On Oct 11, 2011, at 3:04 PM, Ron Greenman wrote:
>
> > NEC requires all metal to be bonded, not grounded (semantics sort of
> > since
> > both go to earth, but there is a difference between bonding and
> > grounding).
> > I'd look it up but have to go to a meeting.
> >
> > On Tue, Oct 11, 2011 at 2:59 PM, Travis Mack, SET
> > <[email protected]>wrote:
> >
> >> There is a local jurisdiction here that requires it.  He tells me
> >> it is in
> >> the NEC.
> >>
> >>
> >> On 10/11/2011 2:58 PM, Steve Leyton wrote:
> >>
> >>> Assuming it's in there somewhere, where does 13 and or 24 speak to
> >>> attaching bonding or grounding wires to sprinkler systems?
> >>> Question
> >>> posed to me today and I had to admit that I don't know ...  hate
> >>> it when
> >>> that happens.
> >>>
> >>>
> >>>
> >>> Steve Leyton
> >>>
> >>> PROTECTION DESIGN&  CONSULTING
> >>>
> >>>
> >>> 2851 Camino del Rio South, Suite 400
> >>>
> >>> San Diego, CA 92108
> >>>
> >>> ------------------------------**------------------------------**-
> >>>
> >>> Ph:      858.751.2930 - ext. 102
> >>>
> >>> Fax:    858.751.2933
> >>>
> >>> Cell:  619.972.5696
> >>>
> >>>
> >>>
> >>>
> >>>
> >>>
> >>>
> >>>
> >>>
> >>> -------------- next part --------------
> >>> An HTML attachment was scrubbed...
> >>> URL:<http://fireball.**firesprinkler.org/mailman/**
> >>> private/sprinklerforum/**attachments/20111011/20e3d0e9/
> >>>
> **attachment.html<http://fireball.firesprinkler.org/mailman/private/spri
> nklerforum/attachments/20111011/20e3d0e9/attachment.html
> >>> >
> >>>>
> >>> ______________________________**_________________
> >>> Sprinklerforum mailing list
> >>> Sprinklerforum@firesprinkler.**org
> >>> <[email protected]>
> >>> http://fireball.firesprinkler.**org/mailman/listinfo/
> >>>
> **sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/spri
> nklerforum
> >>> >
> >>>
> >> ______________________________**_________________
> >> Sprinklerforum mailing list
> >> Sprinklerforum@firesprinkler.**org <[email protected]>
> >> http://fireball.firesprinkler.**org/mailman/listinfo/
> >>
> **sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/spri
> nklerforum
> >> >
> >>
> >
> >
> >
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering Technology
> > Bates Technical College
> > 1101 So. Yakima Ave.
> > Tacoma, WA 98405
> >
> > [email protected]
> >
> > http://www.bates.ctc.edu/fireprotection/
> >
> > 253.680.7346
> > 253.576.9700 (cell)
> >
> > Member:
> > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
> >
> > They are happy men whose natures sort with their vocations. -Francis
> > Bacon,
> > essayist, philosopher, and statesman (1561-1626)
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
> ments/20111011/57cf4803/attachment.html
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
> ments/20111011/7d06e62b/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> CONFIDENTIAL AND PROPRIETARY:
> This email message is intended only for the use of the individual or
entity
> to which it is addressed and may contain information that is privileged
and
> confidential, nor is it, unless specifically stated, intended to be relied
> upon by any person or persons other than the individual or entity named
> above and no warranties or representations are made or intended to persons
> or entities not named above.  If the reader is not the intended recipient,
> you are hereby notified that any dissemination, distribution or copying of
> this communication is strictly prohibited.  If you have received this
> communication in error, please notify us immediately by telephone, return
> this message to the address above and delete all copies.  Thank you.
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
>
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments
/20111012/30a1c076/attachment.html
> >
>  _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111012/311cad55/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to