Understood, however I've seen it used before for this application, right or
wrong. Reading through NFPA-72 seems like the preferred method is a flow
switch that shuts off power instead. Just curious what other people use when
the owner doesn't want any water in the pipe inside the room unless the heat
detector trips if you can't use a solenoid?

Brian Harris, CET
FDFP Inc.
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Sal Izzo
(TECH- 103)
Sent: Wednesday, October 12, 2011 8:50 AM
To: [email protected]
Subject: RE: Solenoid Detail

A solenoid valve by itself is not listed or approved as a controllong valve
for sprinkler systems. They are listed for fire protection service as a
releasing device for deluge valves used for deluge or preaction
applications. It may be used as such when integrally installed as part of an
assembly meeting the deluge valve laboratory standards.

Regards,
Salvatore Izzo, P.E.
Manager-Reliable Technical Services

Sent from my Android phone using TouchDown (www.nitrodesk.com)

-----Original Message-----
From: Brian Harris [[email protected]]
Received: Wednesday, 12 Oct 2011, 8:41am
To: [email protected] [[email protected]]
Subject: Solenoid Detail

Does anybody have a nice detail of a solenoid (pre-action) detail used in
elevator equipment rooms they'd be interested in sharing?



Thanks!



Brian Harris, CET

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507







=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060)
http://www.pctools.com/
=======
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111012/f3ade0db/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111012/46c8cf23/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060)
http://www.pctools.com/
=======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to