Understood, however I've seen it used before for this application, right or wrong. Reading through NFPA-72 seems like the preferred method is a flow switch that shuts off power instead. Just curious what other people use when the owner doesn't want any water in the pipe inside the room unless the heat detector trips if you can't use a solenoid?
Brian Harris, CET FDFP Inc. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Sal Izzo (TECH- 103) Sent: Wednesday, October 12, 2011 8:50 AM To: [email protected] Subject: RE: Solenoid Detail A solenoid valve by itself is not listed or approved as a controllong valve for sprinkler systems. They are listed for fire protection service as a releasing device for deluge valves used for deluge or preaction applications. It may be used as such when integrally installed as part of an assembly meeting the deluge valve laboratory standards. Regards, Salvatore Izzo, P.E. Manager-Reliable Technical Services Sent from my Android phone using TouchDown (www.nitrodesk.com) -----Original Message----- From: Brian Harris [[email protected]] Received: Wednesday, 12 Oct 2011, 8:41am To: [email protected] [[email protected]] Subject: Solenoid Detail Does anybody have a nice detail of a solenoid (pre-action) detail used in elevator equipment rooms they'd be interested in sharing? Thanks! Brian Harris, CET First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060) http://www.pctools.com/ ======= -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20111012/f3ade0db/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20111012/46c8cf23/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060) http://www.pctools.com/ ======= ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060) http://www.pctools.com/ ======= _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum