It's labeled "Elevator Control Room" on the plans.

Brian Harris, CET
FDFP Inc.
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Wednesday, October 12, 2011 11:46 AM
To: [email protected]
Subject: Re: Solenoid Detail

Are you talking about hoist rooms, hydraulic pump rooms, or the shaft?

On Wed, Oct 12, 2011 at 7:17 AM, Brian Harris
<[email protected]>wrote:

> Jim-
> Thanks for the input, does make sense. Have you ever ran across that
> situation where the line running into the room needs to be dry?
>
> Brian Harris, CET
> FDFP Inc.
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, October 12, 2011 10:09 AM
> To: [email protected]
> Subject: RE: Solenoid Detail
>
> Brian,
>
> I was once told by an elevator inspector and another consultant in
> California that they preferred having elevator power shut off (shunt trip)
> by heat detectors rated at less than sprinkler operation because it
> minimizes the chance of accidental shutdown due to waterflow surges,
> testing, etc. It made sense to me.
>
> Since that time it has saved a lot of trouble.
>
> Jim
>
>
> James L (Jim) Roberts, PE/SET |FLUOR|Director-Fire Protection Engineering|
> Central Operations-Building Systems Dept|[email protected]|IODC
> 20.5149
> |864.281.5149|Int-001.864.281.5149|
>
>
>
> From:   "Brian Harris" <[email protected]>
> To:     <[email protected]>
> Date:   10/12/2011 08:53 AM
> Subject:        RE: Solenoid Detail
> Sent by:        [email protected]
>
>
>
> Understood, however I've seen it used before for this application, right
or
> wrong. Reading through NFPA-72 seems like the preferred method is a flow
> switch that shuts off power instead. Just curious what other people use
> when
> the owner doesn't want any water in the pipe inside the room unless the
> heat
> detector trips if you can't use a solenoid?
>
> Brian Harris, CET
> FDFP Inc.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Sal Izzo
> (TECH- 103)
> Sent: Wednesday, October 12, 2011 8:50 AM
> To: [email protected]
> Subject: RE: Solenoid Detail
>
> A solenoid valve by itself is not listed or approved as a controllong
valve
> for sprinkler systems. They are listed for fire protection service as a
> releasing device for deluge valves used for deluge or preaction
> applications. It may be used as such when integrally installed as part of
> an
> assembly meeting the deluge valve laboratory standards.
>
> Regards,
> Salvatore Izzo, P.E.
> Manager-Reliable Technical Services
>
> Sent from my Android phone using TouchDown (www.nitrodesk.com)
>
> -----Original Message-----
> From: Brian Harris [[email protected]]
> Received: Wednesday, 12 Oct 2011, 8:41am
> To: [email protected] [[email protected]]
> Subject: Solenoid Detail
>
> Does anybody have a nice detail of a solenoid (pre-action) detail used in
> elevator equipment rooms they'd be interested in sharing?
>
>
>
> Thanks!
>
>
>
> Brian Harris, CET
>
> First Defense Fire Protection
>
> 11957 Ramah Church Road
>
> Huntersville, NC 28078
>
> Phone: 704.948.3506
>
> Fax: 704.948.3507
>
>
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060)
> http://www.pctools.com/
> =======
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <
>
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
> s/20111012/f3ade0db/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <
>
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
> s/20111012/46c8cf23/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060)
> http://www.pctools.com/
> =======
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060)
> http://www.pctools.com/
> =======
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> ------------------------------------------------------------
> The information transmitted is intended only for the person
> or entity to which it is addressed and may contain
> proprietary, business-confidential and/or privileged material.
> If you are not the intended recipient of this message you are
> hereby notified that any use, review, retransmission, dissemination,
> distribution, reproduction or any action taken in reliance upon
> this message is prohibited. If you received this in error, please
> contact the sender and delete the material from any computer.
>
> Any views expressed in this message are those of the individual
> sender and may not necessarily reflect the views of the company.
> ------------------------------------------------------------
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060)
> http://www.pctools.com/
> =======
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060)
> http://www.pctools.com/
> =======
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111012/dc229878/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060)
http://www.pctools.com/
=======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to