To clarify, there are some proprietary rules in CA from our State OSHA Elevator Department. There are no dry-pipe or other special sprinkler requirements for equipment rooms, except that sprinklers in equipment rooms and elevator pits are required to be under the control of a dedicated shutoff valve, which some jurisdictions require be tamper switched and others don't. In a typical shaft, the only sprinkler is in the pit; even though NFPA 13 doesn't arbitrarily require this sprinkler, every AHJ I've worked with does, based on the potential for accumulation of dust and other combustible refuse. But even in Type V construction where it's typically lined with green board, the shaft is invariably of non-combustible construction, which means that only the pit sprinkler is required by ordinance.
But there's a tweak in the state elevator code requiring that if a sprinkler is installed at the top of the shaft in lieu of a detector, which is an option, then a relay signal from the WFS or FACP is required to be connected to a shunt/trip breaker that kills power to the elevator(s). The whole mess is conditional, but neither a shunt/trip nor a pre-action system or any other special consideration is arbitrarily required, except for the sectional control valve (or valves) for the equipment room and pit sprinklers. Steve Leyton -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, October 12, 2011 7:09 AM To: [email protected] Subject: RE: Solenoid Detail Brian, I was once told by an elevator inspector and another consultant in California that they preferred having elevator power shut off (shunt trip) by heat detectors rated at less than sprinkler operation because it minimizes the chance of accidental shutdown due to waterflow surges, testing, etc. It made sense to me. Since that time it has saved a lot of trouble. Jim James L (Jim) Roberts, PE/SET |FLUOR|Director-Fire Protection Engineering| Central Operations-Building Systems Dept|[email protected]|IODC 20.5149 |864.281.5149|Int-001.864.281.5149| From: "Brian Harris" <[email protected]> To: <[email protected]> Date: 10/12/2011 08:53 AM Subject: RE: Solenoid Detail Sent by: [email protected] Understood, however I've seen it used before for this application, right or wrong. Reading through NFPA-72 seems like the preferred method is a flow switch that shuts off power instead. Just curious what other people use when the owner doesn't want any water in the pipe inside the room unless the heat detector trips if you can't use a solenoid? Brian Harris, CET FDFP Inc. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Sal Izzo (TECH- 103) Sent: Wednesday, October 12, 2011 8:50 AM To: [email protected] Subject: RE: Solenoid Detail A solenoid valve by itself is not listed or approved as a controllong valve for sprinkler systems. They are listed for fire protection service as a releasing device for deluge valves used for deluge or preaction applications. It may be used as such when integrally installed as part of an assembly meeting the deluge valve laboratory standards. Regards, Salvatore Izzo, P.E. Manager-Reliable Technical Services Sent from my Android phone using TouchDown (www.nitrodesk.com) -----Original Message----- From: Brian Harris [[email protected]] Received: Wednesday, 12 Oct 2011, 8:41am To: [email protected] [[email protected]] Subject: Solenoid Detail Does anybody have a nice detail of a solenoid (pre-action) detail used in elevator equipment rooms they'd be interested in sharing? Thanks! Brian Harris, CET First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060) http://www.pctools.com/ ======= -------------- next part -------------- An HTML attachment was scrubbed... URL: < http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachm ent s/20111012/f3ade0db/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum -------------- next part -------------- An HTML attachment was scrubbed... URL: < http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachm ent s/20111012/46c8cf23/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060) http://www.pctools.com/ ======= ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060) http://www.pctools.com/ ======= _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ------------------------------------------------------------ The information transmitted is intended only for the person or entity to which it is addressed and may contain proprietary, business-confidential and/or privileged material. If you are not the intended recipient of this message you are hereby notified that any use, review, retransmission, dissemination, distribution, reproduction or any action taken in reliance upon this message is prohibited. If you received this in error, please contact the sender and delete the material from any computer. Any views expressed in this message are those of the individual sender and may not necessarily reflect the views of the company. ------------------------------------------------------------ _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum