There is little agreement between 72, 13 UMC/IMC, and the elevator guys about all this, but lots of contradictory rules. Going back to my question I don't know what an elevator control room is. Is it a big building with a command center? Is the elevator control panel in a separate room than the rest of the building control panels? Is it the hoist house and control/relay combination that is common? Just curious.
On Wed, Oct 12, 2011 at 9:20 AM, Steve Leyton <[email protected]>wrote: > To clarify, there are some proprietary rules in CA from our State OSHA > Elevator Department. There are no dry-pipe or other special sprinkler > requirements for equipment rooms, except that sprinklers in equipment > rooms and elevator pits are required to be under the control of a > dedicated shutoff valve, which some jurisdictions require be tamper > switched and others don't. In a typical shaft, the only sprinkler is > in the pit; even though NFPA 13 doesn't arbitrarily require this > sprinkler, every AHJ I've worked with does, based on the potential for > accumulation of dust and other combustible refuse. But even in Type V > construction where it's typically lined with green board, the shaft is > invariably of non-combustible construction, which means that only the > pit sprinkler is required by ordinance. > > But there's a tweak in the state elevator code requiring that if a > sprinkler is installed at the top of the shaft in lieu of a detector, > which is an option, then a relay signal from the WFS or FACP is required > to be connected to a shunt/trip breaker that kills power to the > elevator(s). The whole mess is conditional, but neither a shunt/trip > nor a pre-action system or any other special consideration is > arbitrarily required, except for the sectional control valve (or valves) > for the equipment room and pit sprinklers. > > > Steve Leyton > > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of > [email protected] > Sent: Wednesday, October 12, 2011 7:09 AM > To: [email protected] > Subject: RE: Solenoid Detail > > Brian, > > I was once told by an elevator inspector and another consultant in > California that they preferred having elevator power shut off (shunt > trip) > by heat detectors rated at less than sprinkler operation because it > minimizes the chance of accidental shutdown due to waterflow surges, > testing, etc. It made sense to me. > > Since that time it has saved a lot of trouble. > > Jim > > > James L (Jim) Roberts, PE/SET |FLUOR|Director-Fire Protection > Engineering| > Central Operations-Building Systems Dept|[email protected]|IODC > 20.5149 > |864.281.5149|Int-001.864.281.5149| > > > > From: "Brian Harris" <[email protected]> > To: <[email protected]> > Date: 10/12/2011 08:53 AM > Subject: RE: Solenoid Detail > Sent by: [email protected] > > > > Understood, however I've seen it used before for this application, right > or > wrong. Reading through NFPA-72 seems like the preferred method is a flow > switch that shuts off power instead. Just curious what other people use > when > the owner doesn't want any water in the pipe inside the room unless the > heat > detector trips if you can't use a solenoid? > > Brian Harris, CET > FDFP Inc. > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Sal Izzo > (TECH- 103) > Sent: Wednesday, October 12, 2011 8:50 AM > To: [email protected] > Subject: RE: Solenoid Detail > > A solenoid valve by itself is not listed or approved as a controllong > valve > for sprinkler systems. They are listed for fire protection service as a > releasing device for deluge valves used for deluge or preaction > applications. It may be used as such when integrally installed as part > of > an > assembly meeting the deluge valve laboratory standards. > > Regards, > Salvatore Izzo, P.E. > Manager-Reliable Technical Services > > Sent from my Android phone using TouchDown (www.nitrodesk.com) > > -----Original Message----- > From: Brian Harris [[email protected]] > Received: Wednesday, 12 Oct 2011, 8:41am > To: [email protected] [[email protected]] > Subject: Solenoid Detail > > Does anybody have a nice detail of a solenoid (pre-action) detail used > in > elevator equipment rooms they'd be interested in sharing? > > > > Thanks! > > > > Brian Harris, CET > > First Defense Fire Protection > > 11957 Ramah Church Road > > Huntersville, NC 28078 > > Phone: 704.948.3506 > > Fax: 704.948.3507 > > > > > > > > ======= > Email scanned by PC Tools - No viruses or spyware found. > (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060) > http://www.pctools.com/ > ======= > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: > < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachm > ent > s/20111012/f3ade0db/attachment.html> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: > < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachm > ent > s/20111012/46c8cf23/attachment.html> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > > ======= > Email scanned by PC Tools - No viruses or spyware found. > (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060) > http://www.pctools.com/ > ======= > > > > > > ======= > Email scanned by PC Tools - No viruses or spyware found. > (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.18060) > http://www.pctools.com/ > ======= > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > ------------------------------------------------------------ > The information transmitted is intended only for the person > or entity to which it is addressed and may contain > proprietary, business-confidential and/or privileged material. > If you are not the intended recipient of this message you are > hereby notified that any use, review, retransmission, dissemination, > distribution, reproduction or any action taken in reliance upon > this message is prohibited. If you received this in error, please > contact the sender and delete the material from any computer. > > Any views expressed in this message are those of the individual > sender and may not necessarily reflect the views of the company. > ------------------------------------------------------------ > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111012/824a4d78/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum