Non-Quell licensees can buy Tyco K17 SSU's in other than 286*F temperatures. If your building is under 35', you might look at the new extended listings Tyco just issued for their EC25 as a result of some testing at FM last summer. We've got a storage job where the cost is dramatically lower than it would have been with ESFRs, and for the Group A unexpanded commodity we're protecting, they're aces. Two rows per bay in 25' bays, try that with ESFRs :)
If you don't have a need for the upright ESFR, the pendent version is cheaper and more efficient. George L. Church, Jr., CET Rowe Sprinkler Systems, Inc. PO Box 407, Middleburg, PA 17842 877-324-ROWE 570-837-6335 fax [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ronl.Fletcher Sent: Tuesday, November 29, 2011 9:44 AM To: [email protected] Subject: RE: Up-Right ESFR K17 AH One reason to use ESFR uprights is if the system uses raw water the return bends can be avoided. They are more expensive than K17 pendents. Tyco also makes the K17 Ultra used on Quell systems. They cost $10 more than the standard K17 ESFR but have a chrome deflector, otherwise they are identical. I think Viking makes a K17 upright as well. Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Mackinnon Sent: Tuesday, November 29, 2011 7:30 AM To: [email protected] Subject: RE: Up-Right ESFR K17 AH I haven't used them either, but I did do some light reading on the topic recently; Cons: must be raised (sprig's or candle sticks) above piping 3" and larger Pro: eliminate some obstruction rules vs pendent ESFR heads Customer gains more storage room (sprinkler head in upright position vs pendent) Just a few comments... Steven Steven MacKinnon Senior Fire Protection Engineer Hartcorn Plumbing & Heating Inc. 850 South 2nd Street Ronkonkoma, NY 11779 631-580-2300 - Office 631-580-1090 - Fax [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Cesar Lira Sent: Saturday, November 26, 2011 12:00 PM To: [email protected] Subject: Up-Right ESFR K17 AH I Found an Up-Right ESFR K17 Tyco,. but.. Does anyone know when can I use It?,.. if the proper branch line could be an obstruction. Normally or never I have used an Esfr Up-right. Cesar L. -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach ments/20111126/0627770d/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum