Perhaps the "=" is in the extensive testing done by FM demonstrating the
need, or lack thereof, of adding the sprinklers to the calcs?

Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, January 31, 2012 10:25 AM
To: [email protected]
Subject: RE: ESFR Calc 2 hds under obstructions

Cause it sure is tough to come up with written technical substantiation to
support Equivalency when all you do is less.
Same thing Bill Brooks pointed out on larger SF/system, although I'd rather
write something on that, maybe lessening # of valves = less chance one is
shut.
When all you do is omit flow cause the other guy says you can, where's the =
or better?


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, January 31, 2012 9:28 AM
To: [email protected]
Subject: ESFR Calc 2 hds under obstructions

NFPA #13 (2010) 16.2.3.5. Does the ROP/ROC for 2013 NFPA #13 contain any
proposals to drop the requirement to calc an additional 2 heads under
obstructions below ESFR systems as FMG has done?

Ron Fletcher
Aero Automatic
Phoenix, AZ




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1901 / Virus Database: 2109/4778 - Release Date: 01/31/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to