Sounds like you did well there George! (Utilizing the 1' shift rule I'm presuming).
We've had to put in some systems where the under obstruction sprinklers far outnumber the ceiling level sprinklers (slotted cabletrays, piperacks, round ducts....). Damien Shannon Director of Sales and Technical Affairs Provincial Sprinkler Company Ltd. Unit 4, Cork Airport Industrial Estate Kinsale Road, Cork, Ireland. Office: (021) 496 5058 Mobile: (086) 788 8222 Fax: (021) 431 7425 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of George Church Sent: 31 January 2012 19:23 To: [email protected] Subject: RE: ESFR Calc 2 hds under obstructions I couldn't believe the FM 4'x4' rules when we first saw them, fortunately we had flat duct and could go single row 8' o/c. still a lot of EC25 storage sprinklers, but they saved us plenty in the rest of the building (25' bays, 2 lines per instead of three lines of ESFR). George L. Church, Jr., CET Rowe Sprinkler Systems, Inc. PO Box 407, Middleburg, PA 17842 877-324-ROWE 570-837-6335 fax [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Damien Shannon Sent: Tuesday, January 31, 2012 1:37 PM To: [email protected] Subject: RE: ESFR Calc 2 hds under obstructions FM 8-9/2-0 has some pretty extreme requirements for sprinklers under obstructions in storage occupancies. Especially if the obstruction is not a continuous flat bottom (4'x4' max spacing). Obstructions over 2' require sprinklers underneath. I'd say in order to apply the equivalency you'd have to provide all extra requirements that FM specify (and there are quite a lot), to justify eliminating from the calc. And have a AHJ that's willing to go along with the plan. Damien Shannon Director of Sales and Technical Affairs Provincial Sprinkler Company Ltd. Unit 4, Cork Airport Industrial Estate Kinsale Road, Cork, Ireland. Office: (021) 496 5058 Mobile: (086) 788 8222 Fax: (021) 431 7425 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: 31 January 2012 18:04 To: [email protected]; [email protected] Subject: RE: ESFR Calc 2 hds under obstructions That was my thought, after all they do have a requirement for this - if I'm not mistaken, they require you to use the same size branch lines and sprinklers or you do have to perform calculations on these sprinklers. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell www.keyfireprotection.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bob Sent: Tuesday, January 31, 2012 11:59 AM To: [email protected] Subject: RE: ESFR Calc 2 hds under obstructions Perhaps the "=" is in the extensive testing done by FM demonstrating the need, or lack thereof, of adding the sprinklers to the calcs? Bob Knight, CET III 208-318-3057 www.firebyknight.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of George Church Sent: Tuesday, January 31, 2012 10:25 AM To: [email protected] Subject: RE: ESFR Calc 2 hds under obstructions Cause it sure is tough to come up with written technical substantiation to support Equivalency when all you do is less. Same thing Bill Brooks pointed out on larger SF/system, although I'd rather write something on that, maybe lessening # of valves = less chance one is shut. When all you do is omit flow cause the other guy says you can, where's the = or better? George L. Church, Jr., CET Rowe Sprinkler Systems, Inc. PO Box 407, Middleburg, PA 17842 877-324-ROWE 570-837-6335 fax [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Tuesday, January 31, 2012 9:28 AM To: [email protected] Subject: ESFR Calc 2 hds under obstructions NFPA #13 (2010) 16.2.3.5. Does the ROP/ROC for 2013 NFPA #13 contain any proposals to drop the requirement to calc an additional 2 heads under obstructions below ESFR systems as FMG has done? Ron Fletcher Aero Automatic Phoenix, AZ _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ----- No virus found in this message. Checked by AVG - www.avg.com Version: 2012.0.1901 / Virus Database: 2109/4778 - Release Date: 01/31/12 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ----- No virus found in this message. Checked by AVG - www.avg.com Version: 2012.0.1901 / Virus Database: 2109/4778 - Release Date: 01/31/12 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum