FM 8-9/2-0 has some pretty extreme requirements for sprinklers under
obstructions in storage occupancies. Especially if the obstruction is not a
continuous flat bottom (4'x4' max spacing). Obstructions over 2' require
sprinklers underneath. I'd say in order to apply the equivalency you'd have
to provide all extra requirements that FM specify (and there are quite a
lot), to justify eliminating from the calc. And have a AHJ that's willing to
go along with the plan.

Damien Shannon
Director of Sales and Technical Affairs
Provincial Sprinkler Company Ltd.
Unit 4, Cork Airport Industrial Estate
Kinsale Road, 
Cork, Ireland.
Office: (021) 496 5058
Mobile: (086) 788 8222
Fax: (021) 431 7425


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: 31 January 2012 18:04
To: [email protected]; [email protected]
Subject: RE: ESFR Calc 2 hds under obstructions

That was my thought, after all they do have a requirement for this - if I'm
not mistaken, they require you to use the same size branch lines and
sprinklers or you do have to perform calculations on these sprinklers.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob
Sent: Tuesday, January 31, 2012 11:59 AM
To: [email protected]
Subject: RE: ESFR Calc 2 hds under obstructions

Perhaps the "=" is in the extensive testing done by FM demonstrating the
need, or lack thereof, of adding the sprinklers to the calcs?

Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, January 31, 2012 10:25 AM
To: [email protected]
Subject: RE: ESFR Calc 2 hds under obstructions

Cause it sure is tough to come up with written technical substantiation to
support Equivalency when all you do is less.
Same thing Bill Brooks pointed out on larger SF/system, although I'd rather
write something on that, maybe lessening # of valves = less chance one is
shut.
When all you do is omit flow cause the other guy says you can, where's the =
or better?


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, January 31, 2012 9:28 AM
To: [email protected]
Subject: ESFR Calc 2 hds under obstructions

NFPA #13 (2010) 16.2.3.5. Does the ROP/ROC for 2013 NFPA #13 contain any
proposals to drop the requirement to calc an additional 2 heads under
obstructions below ESFR systems as FMG has done?

Ron Fletcher
Aero Automatic
Phoenix, AZ




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1901 / Virus Database: 2109/4778 - Release Date: 01/31/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1901 / Virus Database: 2109/4778 - Release Date: 01/31/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to