The answer is yes - the requirement to include up to two ESFR
sprinklers beneath obstructions has been deleted. See ROP 13-487
The ROP and ROC can be downloaded from www.nfpa.org. CLick on the
COdes and Standards box, then List of standards in the left column
(the second item), then the standard of interest, and finally Next
Edition
Roland
On Jan 31, 2012, at 6:28 AM, <[email protected]> <[email protected]
> wrote:
NFPA #13 (2010) 16.2.3.5. Does the ROP/ROC for 2013 NFPA #13 contain
any proposals to drop the requirement to calc an additional 2 heads
under obstructions below ESFR systems as FMG has done?
Ron Fletcher
Aero Automatic
Phoenix, AZ