Thanks Roland. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Wednesday, February 01, 2012 8:24 AM To: [email protected] Subject: Re: ESFR Calc 2 hds under obstructions
The answer is yes - the requirement to include up to two ESFR sprinklers beneath obstructions has been deleted. See ROP 13-487 The ROP and ROC can be downloaded from www.nfpa.org. CLick on the COdes and Standards box, then List of standards in the left column (the second item), then the standard of interest, and finally Next Edition Roland On Jan 31, 2012, at 6:28 AM, <[email protected]> <[email protected] > wrote: > NFPA #13 (2010) 16.2.3.5. Does the ROP/ROC for 2013 NFPA #13 contain > any proposals to drop the requirement to calc an additional 2 heads > under obstructions below ESFR systems as FMG has done? > > Ron Fletcher > Aero Automatic > Phoenix, AZ > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum