Sounds like we need to do a test. Any grant money out there?
At 11:08 AM 2/1/2012, you wrote: >but the FDC on a sprinkler system is SUPPLEMENTAL and you don't have >to meet the system demand. > >Since one has to also calc the system demand from the FDC, has anyone >looked at the maximum flow they can get through a single 2-way FDC and >still meet their design demand? > >Roland > >On Feb 1, 2012, at 7:52 AM, Steve Leyton wrote: > >>As do a few on the left side. It's common to see demand-based >>requirements for both standpipe and sprinkler systems. How many >>ESFR systems are out there with 2-way FDC's? If system demand is >>1,600gpm ... >> >>SL > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum