Sounds like we need to do a test. Any grant money out there?

At 11:08 AM 2/1/2012, you wrote:
>but the FDC on a sprinkler system is SUPPLEMENTAL and you don't have  
>to meet the system demand.
>
>Since one has to also calc the system demand from the FDC, has anyone  
>looked at the maximum flow they can get through a single 2-way FDC and  
>still meet their design demand?
>
>Roland
>
>On Feb 1, 2012, at 7:52 AM, Steve Leyton wrote:
>
>>As do a few on the left side.  It's common to see demand-based  
>>requirements for both standpipe and sprinkler systems.   How many  
>>ESFR systems are out there with 2-way FDC's?   If system demand is  
>>1,600gpm ...
>>
>>SL
>