Well, that changes my perspective a but doesn't it.

On Wed, Apr 11, 2012 at 1:02 PM, Greg McGahan <[email protected]> wrote:

> The main drain test doesn't necessarily verify the operation of the flow
> switch. If it does, then usually it is a test and drain. And in many cases,
> there is not a huge difference in flow between the 1/2" orifice on test and
> the full 1" orifice when on drain if it is being fed from a stand pipe with
> a pump.
>
> We flow them all, but we get asked why we are flowing so much water when
> the previous inspectors did not. Of course we give them the proper answer
> about doing things right, but I wanted to check ourselves.
>
>
> Greg
>
> On Wed, Apr 11, 2012 at 12:54 PM, <[email protected]> wrote:
>
>> If the individual floor control valves have their own flow switches
>> flowing only one system wouldn't provided verification of operation of the
>> individual flow switches.
>>
>>
>>
>> Craig L. Prahl, CET
>> Fire Protection
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> CH2MHILL Extension  74102
>> [email protected]
>>
>>
>>
>> -----Original Message-----
>> From: [email protected] [mailto:
>> [email protected]] On Behalf Of Greg McGahan
>> Sent: Wednesday, April 11, 2012 1:47 PM
>> To: [email protected]
>> Subject: main drain test
>>
>> When you have a building with multiple floor control valves I have the
>> following question:
>>
>> If the intent of the main drain test is to test the supply, can you
>> accomplish that by flowing the largest or the furtherest from the riser
>> instead of flowing each one individually?
>>
>> Thanks,
>>
>> --
>> Greg McGahan
>> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
>> 1160 McKenzie Road
>> Cantonment, FL 32533
>> 850-937-1850
>> fax 850-937-1852
>> -------------- next part --------------
>> An HTML attachment was scrubbed...
>> URL: <
>> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120411/6df53a7f/attachment.html
>> >
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>
>
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
>
>


-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120411/b42490ac/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to