Jamey,
The main drain test conducted on the incoming water supply to the
building is performed to insure adequacy of the water supply compared to
previous tests. Extreme changes in static or residual pressure will
indicate changes in the municipal supply and/or obstructions in the
piping including closed or partially closed inline valves.

The tests conducted on the sectional valves are done to insure the valve
is still operational (that it will close when required) and the drain
test is done to make sure that it is fully open after you closed it for
the test. This procedure will indicate any dropped gates or broken
valves where the valve appears to be open externally, but it is actually
close internally because it is broken.

rick matsuda
city of dallas

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jamey
Prentice
Sent: Wednesday, April 11, 2012 3:21 PM
To: [email protected]
Subject: RE: main drain test

This one has always confused me, If you are not required to perform a
residual drain test on each sectional valve assembly why does the
manufacturers literature state to do so? Have included Tyco's
requirements
for reference:
The following inspection procedure must be performed as indicated, in
addition to any specific requirements of the NFPA, and any impairment
must
be immediately corrected.
Alarm/Flow Test Procedure
Step 1. Place the test & drain Valve in the "test" position.
Step 2. Fully open the drain valve. Make certain that drainage water
will
not cause any damage or injury.
Step 3. Verify operation of associated alarms.
Step 4. Close the drain valve.
Step 5. Place the test & drain Valve in the "drain" position.
Step 6. Verify that the residual (flowing) pressure indicated by the
pressure gauge is no less that originally recorded for the system when
it
was first installed.
Step 7. Close the drain valve.
Step 8. Verify that the static (not flowing) pressure indicated by the
pressure gauge is no less that originally recorded for the system when
it
was first installed.

Jamey