Jamey,
Yes, you are correct...well at least partially correct. I didn't read
all the previous questions or comments.

Yes, you can do a main drain test to test the supply using the furthest
riser, but you won't be able to determine the exact location of any
obstructions if the test pressures are low...and you still have to
compare the results to previous tests.
However, conducting this one test doesn't mean that you don't have to
test each system individually, too.

The FM system of counting the turns insures that the valve is completely
open/closed, and the drain test insures that it's not broken inside.
rick

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jamey
Prentice
Sent: Wednesday, April 11, 2012 4:12 PM
To: [email protected]
Subject: RE: main drain test

Rick,

That is my  understanding also, but  the original question was " If the
intent of the main drain test is to test the supply, can you accomplish
that
by flowing the largest or the furtherest from the riser instead of
flowing
each one individually? So the answer would be no, because you are not
just
testing the supply?
FM Red Tag actually requires that the valve turns be counted on
open/closed
and system residual pressures be recorded for each closed valve.

 Jamey 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matsuda,
Richard
Sent: Wednesday, April 11, 2012 4:43 PM
To: [email protected]
Subject: RE: main drain test

Jamey,
The main drain test conducted on the incoming water supply to the
building
is performed to insure adequacy of the water supply compared to previous
tests. Extreme changes in static or residual pressure will indicate
changes
in the municipal supply and/or obstructions in the piping including
closed
or partially closed inline valves.

The tests conducted on the sectional valves are done to insure the valve
is
still operational (that it will close when required) and the drain test
is
done to make sure that it is fully open after you closed it for the
test.
This procedure will indicate any dropped gates or broken valves where
the
valve appears to be open externally, but it is actually close internally
because it is broken.

rick matsuda
city of dallas

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jamey
Prentice
Sent: Wednesday, April 11, 2012 3:21 PM
To: [email protected]
Subject: RE: main drain test

This one has always confused me, If you are not required to perform a
residual drain test on each sectional valve assembly why does the
manufacturers literature state to do so? Have included Tyco's
requirements
for reference:
The following inspection procedure must be performed as indicated, in
addition to any specific requirements of the NFPA, and any impairment
must
be immediately corrected.
Alarm/Flow Test Procedure
Step 1. Place the test & drain Valve in the "test" position.
Step 2. Fully open the drain valve. Make certain that drainage water
will
not cause any damage or injury.
Step 3. Verify operation of associated alarms.
Step 4. Close the drain valve.
Step 5. Place the test & drain Valve in the "drain" position.
Step 6. Verify that the residual (flowing) pressure indicated by the
pressure gauge is no less that originally recorded for the system when
it
was first installed.
Step 7. Close the drain valve.
Step 8. Verify that the static (not flowing) pressure indicated by the
pressure gauge is no less that originally recorded for the system when
it
was first installed.

Jamey
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________