If the intent is to prove the backflow at system demand, why shouldn't
the flow be measured if compelling evidence of adequate flow isn't
visually apparent?   If you're a contractor doing service, you need to
have the right tools and accessories.  Sounds to me as if carrying 1.5"
hose with 1.25" NPT x 1.5" NST adapter, or a 2.5" hose with 2" NPT x
2.5" NST adapter, along with a means of measuring flow might be the new
price of a complete inspection including the backflow.        

Steve L.  
Trippin' on pitots




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Greg McGahan
Sent: Monday, July 29, 2013 2:42 PM
To: [email protected]
Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test

Steve,

The probelm is how vague it is - some AHJs want flow Pitot'd, Some say a
2"
main drain is fine for everything, some say prove the size before you
pull a permit....

I simple chart would be awesome - IN THE BOOK - so we have something to
point to.

Greg




On Mon, Jul 29, 2013 at 4:36 PM, Steve Leyton
<[email protected]>wrote:

> The required flow is the highest system demand.  This has been in 25
for
> (somebody help me out here) at least two cycles, I believe?   You can
> use the main drain if you can develop enough flow, you can modify the 
> main drain connection possibly to create multiple connections, you can

> modify and existing riser, put a permanent or temporary valved 
> connection on the downstream side of the backflow (interior or 
> exterior) ... This AIN'T rocket science, y'all.
>
> Steve L.
> Trippin' on da backflows
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Monday, July 29, 2013 2:23 PM
> To: [email protected]
> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test
>
> So basically, nobody has a clue what is really required or how to 
> accurately measure how to properly "exercise" the backflow. Looks like

> 2" main  d rain test works for me until I'm told otherwise. I'll just 
> keep the hose monster in the back of the truck just in case.
>
>
> In a message dated 7/29/2013 5:18:54 P.M. Eastern Daylight Time, 
> [email protected] writes:
>
> This is  kind of like the story where a guy in a bar asks the shapely 
> young thing on  the next barstool if she'd sleep with him for 
> $100,000.00. She answers with  an enthusiastic yes. He then asks if 
> she'd sleep with him for $10.00. Her  response is an indignant, "what 
> do you take me for, a whore?"
> His reply is,  "we've already established that. Now we're just 
> negotiating price."
>
> This was an illustrative metaphor Steve, not a  dirty joke.
>
> We've established that a forward flow is required. And  surprisingly 
> we've actually got a fairly definitive description of what  we're 
> testing for by the committee in the next edition. To me it's in two 
> parts though. First we're not testing so much as "exercising" a 
> component,  which to me is a maintenance issue. In the process though 
> we're also  testing as we're determining if said component is working.
> But when you do  a "test" you need a standard of performance. That 
> brings us to part 2 and  that standard appears to be "at system
demand."
> That requires a measurement  for verification and the comparative 
> baseline standard. So, and to me  only, this new language is as 
> convoluted as the old and doesn't give me a  clear directive. Am I 
> exercising or comparing results, or both? Can I say  that a
> 15 head design, using nominal 1/2 inch orifices has a total surface 
> area of
> 2.94 square inches and a nominal 2 inch main drain has a surface  area

> of
> 3.14 square inches so I'll easily flow as much through my 2 inch  main

> drain as system demand? Or do I have to calculate BOR flow demand,  
> test and measure (pitot or buckey) for flow there at acceptance for 
> verification, and then do that same procedure each year for 
> confirmation?  Or can I just see a good stream from the main drain, 
> note the pressure are  consistent with the acceptance test and 
> say,"That there no backlow thingie  is workin'
> just fine."?
>
>
> On Mon, Jul 29, 2013 at 1:57 PM, Mark A.  Sornsin, P.E. < 
> [email protected]> wrote:
>
> > Depends on  the edition of the standard a local jurisdiction has 
> > adopted, as well  as any local amendments - but yes, forward flow 
> > tests of the backflow  assembly are required by NFPA 13 and 25.
> >
> > Mark A. Sornsin, P.E.  | Karges-Faulconbridge, Inc. | Fire 
> > Protection Engineer | Fargo, ND |  direct: 701.552.9905 | mobile: 
> > 701.371.5759 |
>
> > http://www.kfiengineers.com
> >
> > -----Original Message-----
> >  From: [email protected] [mailto:
> >  [email protected]] On Behalf Of 
> > [email protected]
> > Sent: Monday, July 29, 2013 3:49 PM
> > To:  [email protected]
> > Subject: Re: SIGN for Backflow  Prevention Assembly Forward Flow 
> > Test
> >
> > Is this "forward flow  test" now part of the required code? I was 
> > just
>
> > on
> a
> > job the other  day. New Construction. I noticed that all the systems

> > had a  setup  with (2) 2 1/2" hose valves after the backflow and 
> > alarm
>
> > valve,
> in
> > addition to  the 2" main drain. I take it that these 2 1/2's  are 
> > for this test?
> >
> >
> > In a message dated  7/29/2013 3:57:24 P.M. Eastern Daylight Time, 
> > [email protected]  writes:
> >
> > That  isn't what the intent of the code is as  stated.....just flow 
> > at
>
> > system demand. I can only speak for us, but we  do a LOT of risers 
> > with
> only
> >  a 250 gpm or so demand...sometimes  even less.
> >
> > A 4" drain is well  over what we need to open  it up enough for 
> > system
>
> > demand. I would bet a 2"  drain gets  really close.
> >
> >
> > On Mon, Jul 29, 2013 at 2:52 PM,  David  Autry <[email protected]>
> wrote:
> >
> > >  Wouldn't it be easier, if  you have a 4" backflow preventer you 
> > > run
> 4"
> > > out the wall, 3" BFP, 3"  out the wall, etc...
> >  > That should open her up all the  way.
> > >
> >  >
> > > David Autry
> > >
> > > Meininger Fire   Protection Inc.
> > > 2521 W L St. Suite No.4
> > > Lincoln,  Ne  68522
> > > Voice (402) 466-2616
> > > Fax (402) 466-2617
> > >  [email protected]
> > >
> > >  -----Original Message-----
> > > From:   [email protected]
> > >   [mailto:[email protected]] On 
> > > Behalf Of
> >  Greg
> > > McGahan
> > > Sent: Monday, July 29, 2013 2:35  PM
> > > To:  [email protected]
> > >  Subject: Re: SIGN for Backflow  Prevention Assembly Forward Flow 
> > > Test
> > >
> > > What would be simple and  helpful would be  a table similar to the
> one
> > > used for sizing fire pump   Suction/Discharge/Relief Valve Piping
> etc.
> > >
> > > Since you  are not  measuring pressure, you could say 2" up to X 
> > > gallons, 2.5" for Y  etc....
> > >
> > > A 2-1/2" Main  drain is much easier and cheaper than  some of the 
> > > arrangments left / required on backflow  preventers.
> > >
> >  > Greg
> > >
> > >
> > > On Mon, Jul 29, 2013  at  12:46 PM, Ron Greenman
> > >   <[email protected]>wrote:
> > >
> > > > Better but  it is  still interpretable as requiring a measured 
> > > > flow  be established  (if using the main drain location then the

> > > > BOR
> >  > > design
> > data).
> > > > Then  you'd need a port  that flowed that much, main drain or 
> > > > otherwise,  and  then measure your annual test against 
> > > > anticipated
>
> > > > flow to  make
> > >  > sure you are meeting or exceeding the required  flow. Or am I 
> > > missing
> > > > something? I'm pretty  certain that newer fire service  rated 
> > > > backflows don't  fail any more often than normal FS checks,  and

> > > > that  that type of failure is either catastrophic (doesn't  open
> or  barely
> > > > opens) wouldn't a simple main drain test with   decent flow
> > > > demonstrate that the valve is working? just a  Forum  question 
> > > > as this is a done deal and I wasn't  invited to join the  
> > > > exclusive
> > > > 25 club.
> > >  >
> > > >
> > > > On Mon,  Jul 29, 2013 at 7:11  AM, Roland Huggins
> > > >   <[email protected]>wrote:
> > > >
> > > >  > the  next edition has been cleaned-up on this issue.
> > >  > >
> > > >  >
> > > > _______________________________________________________________
> >  >  > > 25-271
> > > > Log
> > > > > #CP15  Final Action:  Accept
> > > > > (13.6.2.1, 13.6.2.2  (New))
> > > > >
> > > > > ______________________________________________________________
> > > > > _
> > >  >  Submitter:
> > > > > Technical Committee on  Inspection, Testing, and  Maintenance 
> > > > > of
> > > >  Water-Based
> > > > > Systems,
> > >  >  >
> > > > > Recommendation: Revise 13.6.2.1 to read as   follows:
> > > > > 13.6.2.1 All backflow preventers installed in  fire  
> > > > > protection system piping shall be exercised  annually by  
> > > > > conducting a forward flow test at a  minimum flow rate of the
system design.
> > > > > Add new  13.6.2.2 and renumber subsequent  sections
accordingly:
> > > >  > 13.6.2.2 Where hydrants or inside hose  stations are located
> >  > > > downstream of the backflow preventer,  the forward flow  test

> > shall
> > > > > include hose stream demand.   Substantiation: This change was
> > > > > needed to better  reflect  that the backflow preventer is not 
> > > > > a
>
> > > > > precise test whereby  the flow through it must be measured but
> >  > > > effort to exercise  the device at flows as near as  > > 
> > possible
> > > > > to the  system demand.
> >  > > > Committee Meeting Action: Accept
> > > >  >  Number Eligible to Vote: 33
> > > > > Ballot Results:   Affirmative: 32 Negative: 1 Explanation of
> Negative:
> > > >  >
> > >  > > RAY, R.: This proposal should have been  accepted in
principle:
> > > the
> > > > wording
> > >  > > "at a minimum flow rate" is  confusing and should be
reworded.
> > > > >
> > > > > ______________________________________________________________
> > > > > _
> > >  >  > 25-272
> > > > Log
> > > > > #121 Final  Action:  Accept
> > > > >
> > > > >  (13.6.2.1.1)
> > > >  >
> > > > >
> > > > > ______________________________________________________________
> > > > > _
> > >  >  Submitter:
> > > > > Roland J. Huggins, American Fire  Sprinkler  Association, Inc.
> > > > > Recommendation:  Delete the following  text:
> > > > >
> > > > >  13.6.2.1.1 For backflow preventers  sized 2 in. (50 mm) and 
> > > > > under, the forward flow test shall  be acceptable  to conduct 
> > > > > without measuring flow, where the  test  outlet is of a size 
> > > > > to flow the system
> > >  demand.
> > > > >  Substantiation: This section implies that  a measured flow is

> > > > > required for Backflow preventers  (BFP) larger than 2 in when 
> > > > > nothing
> > >   > > in 13.6.2.1
> > > > states
> > > > > such  a  requirement. There are other means to identify that 
> > > > > the
> > >  > > system demand is flowing through the BFP as discussed in
> >  > > > A.13.6.2.1
> > >  > > It also
> > >  > needs
> > > > > to be kept in mind that  we are simply  exercising the BFP to 
> > > > > ensure it
> > > >   will
> > > > > fully open at approximately the system demand. A  high  degree

> > > > > of accuracy regarding the volume of  water is not  warranted.
> > > > > Additionally, BFP's are  subjected to an annual  internal 
> > > > > inspection as  part of the cross
> > > >  connection
> > > > >  protection program. Committee Meeting Action:  Accept Number
> > >  > > Eligible to Vote: 33 Ballot Results:  Affirmative: 33
> >  > > >
> > > > >
> > > > >
> >  >  > > Roland Huggins, PE - VP Engineering
> > > >  >
> > > >  > American Fire Sprinkler Assn.     ---     Fire Sprinklers
Saves
> > >  Lives
> > > > > Dallas,  TX
> > > > >  http://www.firesprinkler.org
> > > > >
> > >  >  >
> > > > >
> > > > >
> > > >  >
> > > >  > On Jul 26, 2013, at 2:57 PM, Dwight  Havens 
> > > > <[email protected]>
> > > >  wrote:
> > > > >
> > >  > > > Then they  ought to say that in the code language.
> > > >  >  >
> > > > > > Dwight
> > > > > >
> >  > >  > >
> > > > > >
> > > > >  >
> > > > > >   ________________________________
> > > > > > From: John  Denhardt  <[email protected]>
> > > > >  > To:  "[email protected]" <
> > > >  >  [email protected]>
> > > > >  > Sent:  Thursday, July 25, 2013 3:07 PM
> > > > > >  Subject: RE: SIGN for  Backflow Prevention Assembly Forward

> > > > > > Flow
> >  > > > > Test
> > >  > > >
> > > >  > >
> > > > > > While I do  disagree to some extent  of what the NFPA 25 
> > > > > > committee  has
> >  > > > done, Roland statement is correct.  I have had   numerous
> > > > > discussions with NFPA 25 committee members  where  they have 
> > > > > stated the intent was to
> >  > >  exercise
> > > > > the device at near system  demand.  The key  word to me was
> > "Exercise".
> > >  > > >
> > > > > >  John
> > > > >  >
> > > > > > John August Denhardt, P.E.,  FSFPE  Strickland Fire 
> > > > > > Protection
>
> > > > > > Incorporated
> >  >  > > > 5113 Berwyn Road
> > > > > > College  Park, Maryland  20740 Office Telephone  Number:
> > > > > > 301-474-1136  Mobile Telephone Number:
> > > >  > > 301-343-1457 FIRE SPRINKLERS  SAVE LIVES - Can you live 
> > > > without
> > > > > > them?
> > > >  >  >
> > > > > > -----Original Message-----
> > > >  >  > From: [email protected]
> [mailto:
> > >  > >  [email protected]] On Behalf Of

> > > Forest
> > > > Wilson
> > > > > > Sent: Thursday,  July 25,  2013 2:42 PM
> > > > > > To:   [email protected]
> > > > > > Subject:  Re:  SIGN for Backflow Prevention Assembly Forward

> > > > > > Flow
> > > >  > > Test
> > > > > >
> > > > > > Here is  an email on this  topic that Roland addressed in 
> > > > > > the
> past:
> > >  > > >
> > > >  > > Im not going to say it was  one of those casual assumptions

> > > > that
> > > > >  > all systems are calculated nor that all risers  have
> placards.
> > > > > > The main thing to keep in mind   that the intent is simply
to
> > > > > > fully EXERCISE the  BFP at  what os expected to be the 
> > > > > > system
>
> > > > > > demand.  If no  data available, a discussion with the AHJ is
> >  > > > > warranted.  As for
> > >  > > >  benchmarks, only the flow is pertinent and pressure is
> >   irrelevant.
> > > > > >
> > > > > >  Roland
> > > >  > >
> > > > > > On Dec  22, 2009, at 2:44 PM, Matthew J.  Willis wrote:
> > > > >  >
> > > > > >>>
> > >  > >  >>> On a more important matter: If a system was retrofitted
> with
> > > a
> > > > > >>> backflow,
> > >  > > >>  and
> > > > > >>> there is no  hydraulic calc plaque attached  to the riser,

> > > > > >>> and
> > > > >  >>> NFPA requires forward flow  testing of backflows, how can

> > > > > you
> > > > > >>> conduct the  test without a  benchmark to test against?
> > > > >  >>>
> >  > > > >>> What is the recommended practice  in this  scenario?
> > > > > >>> Forest Wilson
> > >  >  > >
> > > > > > Sent from my iPhone
> >  > > >  >
> > > > > > On Jul 25, 2013, at  12:16 PM, Ron Greenman 
> > > > > > <[email protected]>
> > > > > wrote:
> > > >  >  >
> > > > > >> Then subjective good flow  demonstrates a  working valve? 
> > > > > >> If so all  the numbers bantered  around are pretty
meaningless.
> > > >  > >>
> > > > >  >>
> > > > >  >>
> > > > > >> On Thu, Jul 25,  2013 at 8:07  AM, Forest Wilson 
> > > > > >> <[email protected]
> > > > > >wrote:
> > > >  >  >>
> > > > > >>> No.
> > > >  > >>> The  intent is not to pitot the output but to exercise  
> > > > the
> valve.
> > > > >  >>>
> > > > >  >>>
> > > > > >>>  Sent from my  iPhone
> > > > > >>>
> > > > >   >>> On Jul 25, 2013, at 10:56 AM, Ron Greenman   >>>
> > > > > <[email protected]>
> > >  > > wrote:
> > >  > > >>>
> > > >  > >>>> Forest. What were  you flowing to discover these
> failures?
> > > > > >>>> Main
> > > >  >  >>>> drain
> > > > > or
> > > >  > >>>>  some special test header? Would a sign with the  data
> > > > > >>>> requested
> > > >   > >>>> by
> > > > the
> > > > >  >>>>  customer that started this thread have had any utility 
> > > > > in  >>>> helping
> > > >  you
> > > > > >>>>  discover the  problem?
> > > > > >>>>
> > > > >   >>>> Then back to that perennial question of what's a "full 
> > > > > flow
>  "
> > > > > >>>> test
> > > >  and
> > > > >  >>> how
> > > > >  >>>> do you do one? I think  Roland said the intent was to 
> > > > > flow an equivalent
> > >  > >  >>> to
> > > > > >>>> the design   discharge criteria. How do you do this? Do
we
> run
> > > > >  >>>> a
> > > > >  >>>> pitot  somewhere on the system? Do we catch and  measure
> > > > > >>>> discharge? If so,  from
> >  > > > >>>> where? How do we arrange the test   port(s)? Do we flow
> the
> > > > > >>>> design
> >  > >  area
> > > > > or
> > > > >  >>>> simulate it  elsewhere? Do we need results of at least  
> > > > > or
> > > > > >>>> better
> > > > >   >>>> flow
> > > > > or
> > > > >  >>>>  right on the money flow? If not either of those how do 
> > > > > we
> > judge?
> > > >  > >>>>
> > >  > > >>>> Doesn't the hydraulic  data plate note the  required psi

> > > per
> > > > > >>>> the   calcs
> > > > > at
> > > > > >>>  the
> > > >  > >>>> BOR and the static? Isn't  the difference the residual 
> > > > drop at  > >>>> that
> > > > >  point
> > >  > > >>>> relative to the design area? Wouldn't  a main  drain 
> > > with good
> > > > > >>>> flow
> > > >  at  a
> > > > > >>> psi
> > > > >  >>>> around  the BOR rating, and returning to close to the 
> > > > > noted  >>>> static
> > > >  when
> > > > > >>>>  terminated suggest a fully  open valve, or an adequately

> > > > > >>>> open
> > > > >   >>>> valve
> > > > if
> > > > > the
> >  > > >  >>>> UG is oversized? In the latter case the  partially open

> > valve
> > > > > is
> > > > >  >>> equivalent
> > > > >  >>>> to fully  open for the system I just described. Am I 
> > > > > missing
> > > >  something
> > > > > >>> here?
> > >  >  > >>>> An erroneous a priori? My understanding of   hydraulics
> wrong?
> > > > > >>>> Main
> > >  > >  drains
> > > > > >>>> are too small  to simulate the result  of all design area
> > > > >  >>>> heads
> > > > flowing
> > > > >  as
> > >  > > >>>> the water passes through the  BOR?
> > > > >  >>>>
> > > > >  >>>>
> > > > >  >>>> On Thu, Jul 25,  2013 at 7:34 AM, Forest Wilson <
> > >  >  [email protected]
> > > > > >>>> wrote:
> >  >  > > >>>>
> > > > >  >>>>> I still have  the check valve from a Ames that  failed 
> > > > > to
> open.
> > > > >  >>>>> It was  jammed shut, discovered when I was called out 
> > > > > because
> > > > > >>>>> they
> > > >  >  >>> couldn't
> > > > > >>>>>  do the fire pump  test.
> > > > >  >>>>>
> > > > >  >>>>> In  another case, I tested a backflow and it failed (on

> > > > > a
>
> > > > > Best
> > > > > >>>>> Buy
> > > > >  >>>  store).
> > > > > >>>>> I  opened the valve up and the  check was damaged, would

> > > > > >>>>> only
> > >  > > >>>>> open  a
> > > > >  >>> third.
> > > > >  >>>>>
> >  > > > >>>>>
> > > > >   >>>>>
> > > > > >>>>> Sent from  my  iPhone
> > > > > >>>>>
> > > >  >  >>>>> On Jul 24, 2013, at 8:53 PM, Ron  Greenman  > >>>>> 
> > > > <[email protected]>
> > > > >  >>>  wrote:
> > > > > >>>>>
> > > >  >  >>>>>> Worked well for plumbing and process  piping 
> > > > applications
> > > > > as
> > > > >  >>>>>> they
> > > >  are
> > > >  > >>>>>> constantly being  exercised.
> > >  > > >>>>>>
> > > > >   >>>>>>
> > > > > >>>>>> On  Wed,  Jul 24, 2013 at 5:12 PM, Dwight Havens <
> > > >  >  [email protected]
> > > > >  >>>>>>  wrote:
> > > > >  >>>>>>
> > > > >   >>>>>>> I do remember the ones with the rods in the   center
> of
> > > > > the
> > > > >  >>>>>>> valve
> > >  > > being
> >  > > > >>>>>>> particularly  poor.
> >  > > > >>>>>>>
> > > > >   >>>>>>> Dwight
> > > > >   >>>>>>>
> > > > >   >>>>>>>
> > > > >   >>>>>>>
> > > > >   >>>>>>>
> > > > >  >>>>>>>  ________________________________
> >  > > >  >>>>>>> From: Ron Greenman   <[email protected]>
> > > > >  >>>>>>>  To:  [email protected]
> > > > >   >>>>>>> Sent: Tuesday, July 23, 2013 11:25 PM
> >  >  > > >>>>>>> Subject: Re: SIGN for  Backflow  Prevention Assembly
> > > Forward
> > > > >  >>>>>>>  Flow
> > > > > Test
> >  > > >  >>>>>>>
> > > > >   >>>>>>>
> > > > >  >>>>>>> By  the mid-nineties you have the early Ames  models
> > > > > >>>>>>> purpose
> >  > > >  >>>>>>> built
> > > > >  for
> > > > >  >>>>>>> sprinklers  readily available, but many units  being 
> > > > > installed
> > > > > >>>>>>> are
> >  >  > > still
> > > > > >>>>>  not
> > > > >  >>>>>>> listed for fire  service as many jurisdictions  don't

> > > > > consider
> > > > > >>>>>>> the
> > >  >  > fire
> > > > > >>>>> line
> >  > > >  >>>>>>> a fire line until after the  backflow, and a n 
> > on-listed
> > > > >  >>>>>>> device is
> > >  > >  >>>>> cheaper
> > > > >   >>>>>>> than a listed one. Plus many go back to the
> seventies
> > > > > and
> > > > >  >>>>>>> many
> > > >  used
> > >  > > >>>>> weights
> > > > >   >>>>>>> instead of springs and complicated lever  systems  
> > > > > for
>
> > > > > joining  >>>>>>> the
> > > >  >  >>>>> clappers
> > > > >   >>>>>>> and weights. Wish I could post a picture.
> >  >  > > >>>>>>>
> > > > >   >>>>>>>
> > > > >  >>>>>>> On  Tue, Jul 23, 2013 at 7:33 PM, Dwight  Havens < 
> > > > > [email protected]
> > >  > > >>>>>>>>  wrote:
> > > > >  >>>>>>>
> > > > >   >>>>>>>> Give me a time frame. My best recollection  is  the

> > > > > mid
> > '90's.
> > > > >  >>>>>>>>
> > > >  >  >>>>>>>> Dwight
> > > > >   >>>>>>>>
> > > > >   >>>>>>>>
> > > > >   >>>>>>>>
> > > > >   >>>>>>>>
> > > > >   >>>>>>>> ________________________________
> > >  >  > >>>>>>>> From: Ron Greenman   <[email protected]>
> > > > >   >>>>>>>> To:   [email protected]
> > > > >   >>>>>>>> Sent: Tuesday, July 23, 2013 9:12 PM
> >  >  > > >>>>>>>> Subject: Re: SIGN for  Backflow  Prevention 
> > Assembly
> > > Forward
> > > > >  >>>>>>>>  Flow
> > > > >  Test
> > > > >  >>>>>>>>
> >  > > >  >>>>>>>>
> > > >  >  >>>>>>>> Were these the plumbing type  before fire  service 
> > > > listed
> > > > >  >>>>>>>>  devices
> > > > >  >>>>> existed.
> > > > >   >>>>>>>>
> > > > >   >>>>>>>>
> > > > >   >>>>>>>> On Tue, Jul 23, 2013 at 4:32 PM, Dwight   Havens <
> > > > > >>> [email protected]
> >  > >  > >>>>>>>>> wrote:
> > >  > >  >>>>>>>>
> > > > >   >>>>>>>>> Yes, yes, and yes.  The  original  proposal was 
> > > > > based on  >>>>>>>>>  observed  >>>>>>> failures
> > > >  >  >>>>>>>>> of BFPAs to operate properly during   main drain
> testing.
> > > > >   >>>>>>>>>
> > > > >   >>>>>>>>> Glendale, AZ public library  specifically  comes 
> > > > > to
> mind.
> > > > >  >>>>>>>>>
> > >  > >  >>>>>>>>> Dwight
> > > > >   >>>>>>>>>
> > > > >   >>>>>>>>>
> > > > >   >>>>>>>>>
> > > > >   >>>>>>>>>
> > > > >   >>>>>>>>> ________________________________
> >  >  > > >>>>>>>>> From: Todd  Williams  <[email protected]>
> > > > >  >>>>>>>>>  To:  "[email protected]" <
> > > > >   >>>>>>>>>   [email protected]>
> > > > >   >>>>>>>>> Sent: Monday, July 22, 2013 9:32   PM
> > > > > >>>>>>>>> Subject: Re:  SIGN  for Backflow Prevention Assembly
> > > > >  >>>>>>>>> Forward
> > > > >   >>>>>>>>> Flow
> > > > > Test
> >  > >  > >>>>>>>>>
> > > >  >  >>>>>>>>>
> > > > >   >>>>>>>>> Has there ever been an instance of  system  
> > > > > failure due to  >>>>>>>>>  the  >>> backflow
> > > > >   >>>>>>> not
> > > > >   >>>>>>>>> properly opening? How about detection  of  a BFP 
> > > > > problem  >>>>>>>>> during  a  full
> > > > > >>>>>>>  flow
> >  > > > >>>>>>>>> test. How about   something subsequent to the
initial
> > > acceptance?
> > > >  >  >>>>>>>>>
> > > > >   >>>>>>>>> Todd G Williams, PE
> > > >  >  >>>>>>>>> Fire Protection  Design/Consulting  Stonington, CT
> > > > >  >>>>>>>>>  860-535-2080
> > > > >  >>>>>>>>>  www.fpdc.com
> > > > >  >>>>>>>>>
> > >  > >  >>>>>>>>>   _______________________________________________
> > > > >   >>>>>>>>> Sprinklerforum mailing list
> > >  >  > >>>>>>>>>   [email protected]
> > > > >   >>>>>>>>>
> > > > >   >>>>>>>>>
> > > > >   >>>>>>>>
> > > > >   >>>>>>>
> > > > >  >>>>>
> > >  > > >>>
> > >  > >
> > > >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > >  >>>>>>>>>   _______________________________________________
> > > > >   >>>>>>>>> Sprinklerforum mailing list
> > >  >  > >>>>>>>>>   [email protected]
> > > > >   >>>>>>>>>
> > > > >   >>>>>>>>>
> > > > >   >>>>>>>>
> > > > >   >>>>>>>
> > > > >  >>>>>
> > >  > > >>>
> > >  > >
> > > >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > >  >>>>>>>>>
> > >  > >  >>>>>>>>
> > > > >   >>>>>>>>
> > > > >   >>>>>>>>
> > > > >   >>>>>>>> --
> > > > >   >>>>>>>> Ron Greenman
> > > > >   >>>>>>>> Instructor
> > > > >   >>>>>>>> Fire Protection Engineering Technology  Bates 
> > > > > Technical
> > > > > >>>>>>>>  College
> > >  > > >>>>>>>> 1101 So.  Yakima Ave.
> > > >  > >>>>>>>>  Tacoma, WA 98405
> > > > >   >>>>>>>>
> > > > >   >>>>>>>> [email protected]
> > > >  >  >>>>>>>>
> > > > >   >>>>>>>>   http://www.bates.ctc.edu/fireprotection/
> > > > >   >>>>>>>>
> > > > >   >>>>>>>> 253.680.7346
> > > > >   >>>>>>>> 253.576.9700 (cell)
> > > >  >  >>>>>>>>
> > > > >   >>>>>>>> Member:
> > > > >   >>>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA,  AFAA,  NIBS, 
> > > > > WSAFM,  >>>>>>>> WFC,
> > >  > WFSC
> >  > > > >>>>>>>>
> > > > >   >>>>>>>> They are happy men whose natures sort  with  their
> > vocations.
> > > > > -Francis
> >  > > >  >>>>>>> Bacon,
> > > >  >  >>>>>>>> essayist, philosopher, and  statesman  (1561-1626)
> > > > >  >>>>>>>>   _______________________________________________
> > > > >   >>>>>>>> Sprinklerforum mailing list   >>>>>>>>
> > > > >  [email protected]
> > > > >   >>>>>>>>
> > > > >   >>>>>>>>
> > > > >   >>>>>>>
> > > > >  >>>>>
> > >  > > >>>
> > >  > >
> > > >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > >  >>>>>>>>   _______________________________________________
> > > > >   >>>>>>>> Sprinklerforum mailing list   >>>>>>>>
> > > > >  [email protected]
> > > > >   >>>>>>>>
> > > > >   >>>>>>>>
> > > > >   >>>>>>>
> > > > >  >>>>>
> > >  > > >>>
> > >  > >
> > > >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > >  >>>>>>>>
> > > >  >  >>>>>>>
> > > > >   >>>>>>>
> > > > >   >>>>>>>
> > > > >  >>>>>>>  --
> > > > >  >>>>>>> Ron Greenman
> > > >  >  >>>>>>> Instructor
> > > > >   >>>>>>> Fire Protection Engineering Technology  Bates 
> > > > > Technical
> > > > > >>>>>>>  College
> > > >  > >>>>>>> 1101 So.  Yakima Ave.
> > > > >  >>>>>>> Tacoma,  WA 98405
> > > > >  >>>>>>>
> >  > > > >>>>>>>   [email protected]
> > > > >  >>>>>>>
> > >  > >  >>>>>>>   http://www.bates.ctc.edu/fireprotection/
> > > > >   >>>>>>>
> > > > >  >>>>>>>  253.680.7346
> > > > >  >>>>>>> 253.576.9700  (cell)
> > > > >  >>>>>>>
> > > > >   >>>>>>> Member:
> > > > >   >>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA,  NIBS, 
> > > > > WSAFM, WFC,  >>>>>>> WFSC
> > > >  >  >>>>>>>
> > > > >   >>>>>>> They are happy men whose natures sort with  their
> vocations.
> > > > > -Francis
> > > > >  >>>>>  Bacon,
> > > > >  >>>>>>> essayist, philosopher,  and statesman  (1561-1626)
> > > > > >>>>>>>  _______________________________________________
> > > > >   >>>>>>> Sprinklerforum mailing list   >>>>>>>
> > > > >  [email protected]
> > >  > >  >>>>>>>
> > > > >   >>>>>>>
> > > > >  >>>>>
> > >  > > >>>
> > >  > >
> > > >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > >  >>>>>>>   _______________________________________________
> > > > >   >>>>>>> Sprinklerforum mailing list   >>>>>>>
> > > > >  [email protected]
> > >  > >  >>>>>>>
> > > > >   >>>>>>>
> > > > >  >>>>>
> > >  > > >>>
> > >  > >
> > > >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > >  >>>>>>>
> > > > >   >>>>>>
> > > > >  >>>>>>
> > >  > >  >>>>>>
> > > > > >>>>>>   --
> > > > > >>>>>> Ron Greenman
> > >  > >  >>>>>> Instructor
> > > > >  >>>>>>  Fire Protection Engineering Technology Bates  
> > > > > Technical
>
> > > > > >>>>>>  College
> > > > > >>>>>>  1101 So. Yakima  Ave.
> > > > > >>>>>> Tacoma, WA   98405
> > > > > >>>>>>
> > > >  >  >>>>>> [email protected]  >  >>>>>>
> > > > >  >>>>>>   http://www.bates.ctc.edu/fireprotection/
> > > > >   >>>>>>
> > > > > >>>>>>   253.680.7346
> > > > > >>>>>>  253.576.9700  (cell)
> > > > >  >>>>>>
> > > > >  >>>>>>  Member:
> > > > > >>>>>>  ASEE, SFPE,  ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, 
> > > > > >>>>>> WSAFM,
> > > > >  >>>>>> WFC,
> > > > >   >>>>>> WFSC
> > > > >   >>>>>>
> > > > > >>>>>> They  are  happy men whose natures sort with their
> vocations.
> > >  >  -Francis
> > > > > >>>>> Bacon,
> >  > > >  >>>>>> essayist, philosopher, and  statesman  (1561-1626)
> > > > >  >>>>>>   _______________________________________________
> > > > >   >>>>>> Sprinklerforum mailing list   >>>>>>
> > > > >  [email protected]
> > > >  >  >>>>>>
> > > > > >>>>>
> >  >  > > >>>
> > > > >
> > >  >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > >  >>>>>   _______________________________________________
> > > > >   >>>>> Sprinklerforum mailing list   >>>>>
> > > > >  [email protected]
> > > > >   >>>>>
> > > > > >>>>>
> > >  > >  >>>
> > > > >
> > > >
> >  > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >  > > kl
> > >  > er.org
> > > > >  >>>>>
> > > > >  >>>>
> >  > > > >>>>
> > > > >   >>>>
> > > > > >>>> --
> > > >  >  >>>> Ron Greenman
> > > > >  >>>>  Instructor
> > > > > >>>> Fire  Protection Engineering  Technology Bates Technical
> > > > >  >>>> College
> > > > > >>>> 1101  So.  Yakima Ave.
> > > > > >>>> Tacoma, WA  98405
> > > >  > >>>>
> > > > >  >>>>  [email protected]  >>>>  >>>>  
> > > > > http://www.bates.ctc.edu/fireprotection/
> > > > >   >>>>
> > > > > >>>> 253.680.7346
> >  > >  > >>>> 253.576.9700 (cell)
> > > >  >  >>>>
> > > > > >>>>  Member:
> > > > >  >>>> ASEE, SFPE, ASCET, NFPA,  AFSA, NFSA, AFAA, NIBS, WSAFM,

> > > > > WFC,
> > > >  > >>>> WFSC
> > > > >   >>>>
> > > > > >>>> They are happy men  whose  natures sort with their
> vocations.
> > > > >  >>>>  -Francis
> > > > > >>>  Bacon,
> > > > >  >>>> essayist, philosopher,  and statesman (1561-1626)
> > > >  > >>>>  _______________________________________________
> > >  > >  >>>> Sprinklerforum mailing list
> > > > >   >>>> [email protected]
> > > >  >  >>>>
> > > > > >>>
> > >  > >
> > > >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > >  >>>  _______________________________________________
> >  > > > >>>  Sprinklerforum mailing list
> > >  > > >>>  [email protected]
> >  > > > >>>
> > >  > > >>>
> >  > > >
> > > >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > >  >>>
> > > > > >>
> > >  > >  >>
> > > > > >>
> > > > > >>   --
> > > > > >> Ron Greenman
> > > > >  >>  Instructor
> > > > > >> Fire Protection  Engineering Technology  Bates Technical 
> > > > > >> College
> > > > >  >> 1101 So. Yakima  Ave.
> > > > > >> Tacoma, WA  98405
> > > > >  >>
> > > > > >>  [email protected]
> > > > >  >>
> > >  > > >>  http://www.bates.ctc.edu/fireprotection/
> > >  > > >>
> > >  > > >> 253.680.7346
> >  > > > >> 253.576.9700  (cell)
> > > > >  >>
> > > > > >> Member:
> > >  > >  >> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM,
> WFC,
> > > WFSC
> > > > > >>
> > > > >  >> They are happy  men whose natures sort with their
> vocations.
> > > > > >>  -Francis
> > > >  > Bacon,
> > > > > >> essayist,  philosopher, and  statesman (1561-1626) 
> > > > > >> _______________________________________________
> > > > >  >>  Sprinklerforum mailing list  >> 
> > > > > [email protected]
> > > > >  >>
> > > >  >
> > > >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > > >   _______________________________________________
> > > > >  >  Sprinklerforum mailing list
> > > > > >   [email protected]
> > > > > >
> >  > >  >
> > > >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > > >   _______________________________________________
> > > > >  >  Sprinklerforum mailing list
> > > > > >   [email protected]
> > > > > >
> >  > >  >
> > > >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > > >   _______________________________________________
> > > > >  >  Sprinklerforum mailing list
> > > > > >   [email protected]
> > > > > >
> >  > >  >
> > > >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > >
> >  > > >  _______________________________________________
> >  > > >  Sprinklerforum mailing list
> > > > >   [email protected]
> > > > >
> > >  >  >
> > > >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > > >
> >  > >
> > > >
> > > >
> > >  >  --
> > > > Ron Greenman
> > > > Instructor
> > >  > Fire  Protection Engineering Technology Bates Technical  
> > > College
> > > > 1101  So. Yakima Ave.
> > > > Tacoma,  WA 98405
> > > >
> > > >   [email protected]
> > > >
> > > >   http://www.bates.ctc.edu/fireprotection/
> > > >
> > >  >  253.680.7346
> > > > 253.576.9700 (cell)
> > >  >
> > > >  Member:
> > > > ASEE, SFPE, ASCET,  NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM,  WFC, 
> > > > WFSC
> > > >
> >  > > They are happy men whose natures sort with  their  vocations.
> > > > -Francis Bacon, essayist, philosopher, and   statesman
(1561-1626)
> > > >  _______________________________________________
> > > >  Sprinklerforum  mailing list
> > > >  [email protected]
> > >  >
> > >  >
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fires
> > > > pr
> > > > in
> >  > > kl
> > >  > er.org
> > > >
> >  >
> > >
> > >
> > > --
> > > Greg   McGahan
> > > Living Water Fire Protection, LLC   <http://www.livingwaterfp.com>
> > > 1160 McKenzie Road
> >  >  Cantonment, FL 32533
> > > 850-937-1850
> > > fax  850-937-1852
> > >   _______________________________________________
> > > Sprinklerforum  mailing  list
> > > [email protected]
> >  >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .o
> >  >  rg
> > >  _______________________________________________
> > >   Sprinklerforum mailing list
> > >   [email protected]
> > >
> >  >
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> >  >
> >
> >
> >
> > --
> > Greg McGahan
> > Living  Water Fire Protection, LLC  <http://www.livingwaterfp.com>
> >  1160 McKenzie Road
> > Cantonment, FL  32533
> >  850-937-1850
> > fax  850-937-1852
> >  _______________________________________________
> > Sprinklerforum   mailing  list
> >  [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> >
> >  _______________________________________________
> > Sprinklerforum mailing  list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> >
> >
> > ____________________________________________________________________
> > __  This email has been scanned by the Symantec Email Security.cloud
> service.
> > For more information please visit
> http://www.symanteccloud.com__________________________________________
> __
> __________________________
> >  _______________________________________________
> > Sprinklerforum mailing  list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering  Technology Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA  98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700  (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS,  WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their  vocations. -Francis 
> Bacon, essayist, philosopher, and statesman  (1561-1626) 
> _______________________________________________
> Sprinklerforum  mailing  list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to