Hello All,

Last time I looked the only one I found listed for branch lines routing it next 
to the heads was the Tyco Raychem system. Yes the controller was nice to 
install and program, You pay the price for that too. The one I installed covers 
2 sections of pipe. I put the temp sensor on the smaller pipe and have not had 
any problems in the 4 years it has been in service.

Thursday, August 1, 2013, 3:03:02 PM, you wrote:

> Steve,

>  I had priced a system about two years ago and learned a lot. I found the
> Tyco Raychem system was the best for my scenario; a lot of factors go in to
> it - depends on size of piping and length, how much (if any) insulation
> will be used, temperatures, and don't forget it has to be listed for FP and
> supervised per NFPA 13. We had a local Tyco distributor work up the pricing
> - we gave him our plans and he took it off and priced it. I'm glad he did.
> I would have missed a lot - this was a big system in a 100'-0+ tower
> w/standpipes etc.. It ended up needing two panels for supervisory due to
> the length of the cables, etc.

> Bobby


> On Thu, Aug 1, 2013 at 1:53 PM, Steve Leyton
> <[email protected]>wrote:

>> Help a warm weather brother out please, with recommendations for heat
>> trace systems.   Price, reliability, branch line listings?



>> Steve Leyton

>> PROTECTION DESIGN & CONSULTING

>> 2851 Camino del Rio South, Suite 400

>> San Diego, CA 92108

>> -------------------------------------------------------------

>> Ph:      858.751.2930 - ext. 102

>> Fax:    858.751.2933

>> Cell:  619.972.5696









>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]

>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org







-- 
Best regards,
 Charles                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to