I'm assuming he wants to/has to install sprinklers. Install a flat ceiling over the storage and go from there.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com On Sep 16, 2013, at 1:13 PM, teemsprinkdave <[email protected]> wrote: > NFPA 13, 2007 ed. chap.12.1.2, ...system criteria specified in this chapter > is intended for ceiling slopes NOT MORE than 2 in 12. I've got a customer > storing 20' on racks, unsprinklered building, and have a slope more than 2 in > 12. Is there an option I'm missing?? > > DAVE GROVER > Teem Sprinkler Co. > Superintendent > NFPA 25 Level II Inspector > P 336-650-9005 > F 336-650-9007 > C 336-399-9006 > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org