yes, FM, wanting sprinklers. Approx. 6000 sq. ft. area with this ceiling slope. 
Thought of flat ceiling, but wanted to make sure I didn't miss anything. thanks


DAVE 

From: Todd - Work <[email protected]>
To: "[email protected]" 
<[email protected]> 
Sent: Monday, September 16, 2013 1:23 PM
Subject: Re: ceiling slope


I'm assuming he wants to/has to install sprinklers. Install a flat ceiling over 
the storage and go from there.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
http://www.fpdc.com/

On Sep 16, 2013, at 1:13 PM, teemsprinkdave <[email protected]> 
wrote:

>  NFPA 13, 2007 ed. chap.12.1.2, ...system criteria specified in this chapter 
>is intended for ceiling slopes NOT MORE  than 2 in 12.  I've got a customer 
>storing 20' on racks, unsprinklered building, and have a slope more than 2 in 
>12. Is there an option I'm missing?? 
>  
> DAVE GROVER
> Teem Sprinkler Co.
> Superintendent 
> NFPA 25 Level II Inspector