You might check the factory mutual design guides. I think they have some 
criteria for storage under sloped ceilings- not sure though.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
teemsprinkdave
Sent: Monday, September 16, 2013 12:35 PM
To: [email protected]
Subject: Re: ceiling slope

yes, FM, wanting sprinklers. Approx. 6000 sq. ft. area with this ceiling slope. 
Thought of flat ceiling, but wanted to make sure I didn't miss anything. thanks


DAVE 

From: Todd - Work <[email protected]>
To: "[email protected]" 
<[email protected]> 
Sent: Monday, September 16, 2013 1:23 PM
Subject: Re: ceiling slope


I'm assuming he wants to/has to install sprinklers. Install a flat ceiling over 
the storage and go from there.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
http://www.fpdc.com/

On Sep 16, 2013, at 1:13 PM, teemsprinkdave <[email protected]> 
wrote:

>  NFPA 13, 2007 ed. chap.12.1.2, ...system criteria specified in this chapter 
>is intended for ceiling slopes NOT MORE  than 2 in 12.  I've got a customer 
>storing 20' on racks, unsprinklered building, and have a slope more than 2 in 
>12. Is there an option I'm missing?? 
>  
> DAVE GROVER
> Teem Sprinkler Co.
> Superintendent 
> NFPA 25 Level II Inspector
> P 336-650-9005
> F 336-650-9007
> C 336-399-9006
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to