Reference to Factory Mutual Data Sheet 2.0 clause 2.2.1.6 gives their take
up to 20deg.slope. Use IRS over 10deg.


Russell Gregory
Christchurch NZ
e-mail [email protected]
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
teemsprinkdave
Sent: Tuesday, 17 September 2013 5:35 AM
To: [email protected]
Subject: Re: ceiling slope

yes, FM, wanting sprinklers. Approx. 6000 sq. ft. area with this ceiling
slope. Thought of flat ceiling, but wanted to make sure I didn't miss
anything. thanks


DAVE 

From: Todd - Work <[email protected]>
To: "[email protected]"
<[email protected]> 
Sent: Monday, September 16, 2013 1:23 PM
Subject: Re: ceiling slope


I'm assuming he wants to/has to install sprinklers. Install a flat ceiling
over the storage and go from there.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
http://www.fpdc.com/

On Sep 16, 2013, at 1:13 PM, teemsprinkdave <[email protected]>
wrote:

>  NFPA 13, 2007 ed. chap.12.1.2, ...system criteria specified in this
chapter is intended for ceiling slopes NOT MORE  than 2 in 12.  I've got a
customer storing 20' on racks, unsprinklered building, and have a slope more
than 2 in 12. Is there an option I'm missing?? 
>  
> DAVE GROVER
> Teem Sprinkler Co.
> Superintendent 
> NFPA 25 Level II Inspector
> P 336-650-9005
> F 336-650-9007
> C 336-399-9006
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to