Haven't yet. We're thinking run in, sprinklers, ceiling, tenet may op. to lease 
somewhere else. But we're checking, thanks for all the help.


DAVE GROVER
Teem Sprinkler Co.
Superintendent 
NFPA 25 Level II Inspector
P 336-650-9005
F 336-650-9007
C 336-399-9006

From: Matt Grise <[email protected]>
To: "[email protected]" 
<[email protected]> 
Sent: Monday, September 16, 2013 3:15 PM
Subject: RE: ceiling slope


Have you discussed a factory mutual design with the fire marshal? Many 
jurisdictions will allow FM designed systems.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
teemsprinkdave
Sent: Monday, September 16, 2013 2:13 PM
To: [email protected]
Subject: Re: ceiling slope

Fire Marshal not factory mutual. thanks anyway.


DAVE

From: David Autry <[email protected]>
To: [email protected] 
Sent: Monday, September 16, 2013 2:20 PM
Subject: RE: ceiling slope


If it's a FM job they should have all the design criteria you should ever
hope to have.


David Autry

Meininger Fire Protection Inc.
2521 W L St. Suite No.4
Lincoln, Ne 68522
Voice (402) 466-2616
Fax (402) 466-2617
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
teemsprinkdave
Sent: Monday, September 16, 2013 12:35 PM
To: [email protected]
Subject: Re: ceiling slope

yes, FM, wanting sprinklers. Approx. 6000 sq. ft. area with this ceiling
slope. Thought of flat ceiling, but wanted to make sure I didn't miss
anything. thanks


DAVE

From: Todd - Work <[email protected]>
To: "[email protected]"
<[email protected]>
Sent: Monday, September 16, 2013 1:23 PM
Subject: Re: ceiling slope


I'm assuming he wants to/has to install sprinklers. Install a flat ceiling
over the storage and go from there.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
http://www.fpdc.com/

On Sep 16, 2013, at 1:13 PM, teemsprinkdave <[email protected]>
wrote:

>  NFPA 13, 2007 ed. chap.12.1.2, ...system criteria specified in this
chapter is intended for ceiling slopes NOT MORE  than 2 in 12.  I've got a
customer storing 20' on racks, unsprinklered building, and have a slope
more than 2 in 12. Is there an option I'm missing??
>
> DAVE GROVER
> Teem Sprinkler Co.
> Superintendent
> NFPA 25 Level II Inspector
> P 336-650-9005
> F 336-650-9007
> C 336-399-9006
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to