In a BUILDING that requires sprinkler not sure how you don't put them in the 
wash bay.  I can't think of an exception. Standard NFPA 13 about corrosive 
environments, yes you need to do something. 

Chris Cahill, PE*
Senior Fire Protection Engineer 
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Wednesday, December 04, 2013 2:32 PM
To: [email protected]
Subject: RE: Heads in Car Wash

We recently completed a car wash. 

We had to sprinkle the machine, electrical, and convenience store rooms. The 
actual wash bay was excluded. Owner paid for all galvanized schedule 40 pipe 
and stainless steel sprinkler heads. They had originally considered stainless 
steel piping.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd 
Letterman
Sent: Wednesday, December 04, 2013 2:27 PM
To: [email protected]
Cc: [email protected]
Subject: Re: Heads in Car Wash

Hi Brian you didn't say where it was, how big or what code your under, but if 
you go to definitions under the IBC A-5 occupancy will see car washes. Then go 
to 903.2.1.5 and you will see when sprinklers are required if where you are at 
is under the 2009 IBC.

Sent from my iPad

> On Dec 4, 2013, at 11:51 AM, "Brian Harris" <[email protected]> wrote:
> 
> Quoting a large auto dealership that has a drive thru car wash attached to 
> the side of the building. I can't find anything in the code specifically 
> dealing with a car wash but for some reason it just seems strange to add 
> heads to a carwash, yes/no?  Also, if they are required which my gut says 
> they are is there a concern about corrosion & rust? Thanks!
> 
> Brian Harris, CET
> BVS Systems Inc.
> Sprinkler Division
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to