We did a county garage and were required to protect the car wash bay. I
could not find  way out of it....

Greg


On Wed, Dec 4, 2013 at 2:49 PM, Cahill, Christopher <[email protected]>wrote:

> In a BUILDING that requires sprinkler not sure how you don't put them in
> the wash bay.  I can't think of an exception. Standard NFPA 13 about
> corrosive environments, yes you need to do something.
>
> Chris Cahill, PE*
> Senior Fire Protection Engineer
> Burns & McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
>
> Proud to be one of FORTUNE's 100 Best Companies to Work For
> *Registered in: MN
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Matt Grise
> Sent: Wednesday, December 04, 2013 2:32 PM
> To: [email protected]
> Subject: RE: Heads in Car Wash
>
> We recently completed a car wash.
>
> We had to sprinkle the machine, electrical, and convenience store rooms.
> The actual wash bay was excluded. Owner paid for all galvanized schedule 40
> pipe and stainless steel sprinkler heads. They had originally considered
> stainless steel piping.
>
> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.927.0222 cell
> www. AFPsprink.com
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Todd
> Letterman
> Sent: Wednesday, December 04, 2013 2:27 PM
> To: [email protected]
> Cc: [email protected]
> Subject: Re: Heads in Car Wash
>
> Hi Brian you didn't say where it was, how big or what code your under, but
> if you go to definitions under the IBC A-5 occupancy will see car washes.
> Then go to 903.2.1.5 and you will see when sprinklers are required if where
> you are at is under the 2009 IBC.
>
> Sent from my iPad
>
> > On Dec 4, 2013, at 11:51 AM, "Brian Harris" <[email protected]>
> wrote:
> >
> > Quoting a large auto dealership that has a drive thru car wash attached
> to the side of the building. I can't find anything in the code specifically
> dealing with a car wash but for some reason it just seems strange to add
> heads to a carwash, yes/no?  Also, if they are required which my gut says
> they are is there a concern about corrosion & rust? Thanks!
> >
> > Brian Harris, CET
> > BVS Systems Inc.
> > Sprinkler Division
> > bvssystemsinc.com<http://bvssystemsinc.com/>
> > Phone: 704.896.9989
> > Fax: 704.896.1935
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to